Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Testing SNMP alarms

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Testing SNMP alarms
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • DavidFisher
    DavidFisher
  • Dave_Shore
    Dave_Shore
  • RobertAndriolo
    RobertAndriolo
  • Benji
    Benji
  • CraigEl
    CraigEl
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
6537 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Testing SNMP alarms

Picard Product_Support
‎2018-09-11 01:04 PM

Issue

There is no full end to end description on how to test SNMP alarms in SmartStruxure 1.6.1 and later

Product Line

EcoStruxure Building Operation

Environment

  • SNMP
  • Alarms

Cause

Only a guide on how to create the SNMP alarms is available, but there is no guide available on how to test them.

For general information regarding SNMP traps, refer to the following Web Help links:

Versions 1.6 and 1.7

  • SNMP Notification Properties
  • Create SNMP Notification Wizard – SNMP Notification Page
  • SNMP Notification View

Version 1.8 and later

  • SNMP Notification Distribution Method
  • Create Notification Wizard - Configure SNMP Page

Resolution

  1. Download and install "MIB Browser" from iReasoning
  2. Download the mib file for SmartStruxure
  3. Load the SmartStruxure mib file into the MIB Browser through "File"-->"Load MIBs", and select the SmartStruxure mib file
  4. Create a simple alarm in SmartStruxure and make it trigger on a digital point
  5. Create a SNMP notification with the following settings. To get to the conditions/filter, open (double click on it or hit enter) the SNMP notification. Only showing the properties of it will not show the filter settings.
    • "Address" is the address of the SNMP manager that receives the SNMP notification, in this test "localhost" since the SNMP manager is installed locally.
    • "User name" is the user name of the user on the SNMP manager that receives the notification.
    • In filter settings, select normal and alarm state, and add "Source server = *" as a condition
  6. In the MIB browser, select "Tools"-->"Trap Receiver"
  7. Trigger the alarm in SmartStruxure
  8. An alarm will now be seen in the MIB browsers trap receiver window
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 17483
  • DavidShore19
Was this article helpful? Yes No
100% helpful (4/4)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of