System alarm message, Physical device not defined/configured, in the alarm window.
TAC Vista
TAC Vista (all versions)
TAC Xenta programmable controllers
This message is displayed when there is a TAC Xenta 401/30x/28x that is attached to the physical network, but the name is not in the TAC Vista database. It is there to alert that there are unconfigured controllers on the network.
  • Download to the controller from TAC Vista
  • Remove the controller if it is not needed.
For an alternative cause and resolution for the message, see Physical device not defined/configured.