SHD100 / SHD101 - Humidity Sensors can give a DC voltage signal of greater than 10 Volts.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SHD100 / SHD101 - Humidity Sensors can give a DC voltage signal of greater than 10 Volts.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1549 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SHD100 / SHD101 - Humidity Sensors can give a DC voltage signal of greater than 10 Volts.

Picard Product_Support
‎2018-09-06 02:12 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-08 06:17 PM

Issue

When using SHD100 or SHD101 humidity sensors with a BAS 2800+ Outstation or Sigma Controller, the sensors may output a DC voltage exceeding the expected 0–10V range. This can cause the controller to display a default or erroneous value.

Product Line

Satchwell BAS & Sigma

Environment

  • BAS 2800+ Outstation
  • Sigma Controller
  • SHD100 / SHD101 Humidity Sensors

Cause

The sensors are capable of producing a DC voltage signal greater than 10V. When this occurs, the controller may interpret the signal as out-of-range and revert to a default value, potentially triggering alarms or incorrect readings.

Resolution

To prevent out-of-range errors and ensure accurate readings:

  1. Add a Series Resistor

    Install a 10K ohm, 0.1% tolerance resistor in series with the 0–10V signal line. This helps limit the voltage and protect the input circuitry.

  2. Create a Lookup Table

    In Sigma or BAS 2800+, configure a lookup table with the following values:

    Input (mV) Output (%)
    0 0
    83335 100
    100000 100

    This table allows the system to interpret voltages up to 11.335V without triggering an out-of-range alarm.

  3. Apply the Table

    Assign the lookup table to the analog input object. Then download both the object and the table to the Outstation or Controller.


Outcome

With this configuration, the system will tolerate sensor outputs up to 11.335V, ensuring stable operation and avoiding false alarms.

Labels (2)
Labels:
  • Field Devices
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 4589
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore