Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Programming SNVT_Switch in Menta

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Programming SNVT_Switch in Menta
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3084 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Programming SNVT_Switch in Menta

Picard Product_Support
‎2018-09-06 02:21 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:59 AM

Issue

Instructions and programming example for using SNVT_Switch as an input or output in Menta

Product Line

TAC Vista, EcoStruxure Building Operation

Environment

  • Menta
  • Function Block

Cause

The attached programming example is intended to clarify how to properly use SNVT_Switch in Menta.

SNVT_Switch is a structured SNVT with two attributes, or members, State and Value. Programmatically this will be one SNVT in the device template, but it will be programmed as two separate analog points in Menta. These two public blocks will have different names in Menta, but they will share the same SNVT name with the exception of one of the points being the state member, and the other being the value member.

It is important to remember that these points must always be programmed as analog points in Menta. AI's for input points, and AO's for output points. The state attribute is intended to be used for a binary on-off signal, but also contain the value -1 for Invalid value. The value attribute is intended to be used as a 0-100% signal.

This SNVT is typically used in the market for starting and stopping a VFD drive and sending a speed reference with the same SNVT. The 0,1 value on the state member will start and stop the drive, and the value member will send a 0-100% speed signal.

Resolution

Please see the attached Menta macro as a guide to using SNVT_Switch in Menta. This example shows you SNVT_Switch as an input and as an output to the Xenta controller.

To use this macro please follow these steps:

  1. Download the attached macro from above.
  2. Unzip the file and extract the SNVT_Switch.MTA from the archive to the local hard drive.
  3. Open Menta
  4. Right-click in Menta and click Load Macro
  5. Browse to the SNVT_Switch.MTA on the local hard drive and open it. It should import into the Menta file that is open.
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Attachments
SNVT_SWITCH.zip
Tags (2)
  • Find more articles tagged with:
  • 4441
  • MikaelKrantz19
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore