Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

No more address table slots for a device involved in the attempted connection. (Subsystem: NS Connections, #15)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • No more address table slots for a device involved in the attempted connection. (Subsystem: NS Connections, #15)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2217 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

No more address table slots for a device involved in the attempted connection. (Subsystem: NS Connections, #15)

Picard Product_Support
‎2018-09-07 03:41 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:23 AM

Issue

NSConnections15.png

No more address table slots for a device involved in the attempted connection. (Subsystem:  NS Connections, #15)

Product Line

TAC Vista

Environment

LonMaker 3.X

NS Connections Error codes are not specific to any one LON environment, the display of the error may vary, but the steps to resolve should be the same.
 

Cause

Every LON Neuron chip has 15 total address table slots inside, which store addressing information for SNVT communication.  Xenta programmable controllers utilize Address Table slots 0 and 1 for TAC and Xenta Group Binding information for reporting online status to the Vista Server and transferring TA Network Variables to each other.  This leaves 13 available address table slots in a Xenta programmable controller.  There are many scenarios by which address table slots are consumed (both in the sending and receiving controllers).  If you have exceeded the address table limitations, no further SNVT bindings (which would require additional address table slots) will be allowed.
 

Resolution

The error message should indicate which controller has exceeded its address table limitations (sending or receiving).  First verify the current status of the address table.

  1. Right-click on the controller
  2. Select Properties
  3. Navigate to the Address Table tab.

    fulladdresstable.png

     

  4. This will tell you (a) if the address table is indeed full or (b) how many slots you have left.  Knowing this can help you determine the easiest recourse to the problem.

If the address table is full in the sending controller:

  1. Information can only be sent via one-to-one bindings to 15 controllers (13 from a Xenta programmable).  Sometimes combining data into a one-to-many can save address table slots.  Instead of sending an individual occupancy to 20 VAVs, which consumes 20 address table slots, send them all the same one-to-many occupancy command, which consumes only 1 address table slot.
  2. Using a broadcast SNVT binding type will save on address table slots by only consuming one slot per receiving subnet instead of one per receiving controller.  This will increase network bandwidth, but allows one-to-one bindings to many controllers in the same subnet.  Xenta programmable SNVT output limits would be the only limiting factor.

    See Bind to more than 13 unique LON devices without running out of address table entries for details on creating Broadcast SNVT Bindings.

If the address table is full in the receiving controller:

  1. If the binding is a one-to-one binding type:
    1. This is typically not an issue. The receiving controller does not normally have an address table slot consumed by a one-to-one SNVT binding. The only time a receiving controller has an address table slot consumed by a one-to-one SNVT binding is if that SNVT input is set to ""Poll."" (Unacknowledged, repeated, acknowledged profiles have no bearing on the number of address table slots consumed by one-to-one bindings.)

      uncheckpoll.png

       

    2. Unless dictated by the manufacturer of the device with which you are integrating, it is very rare to require polled inputs in a Menta file. Check the SNVT AI blocks in Menta and uncheck the "Poll" checkbox. Binding these inputs will no longer consume an address table slot in the receiving controller.
  2. If the binding is a one-to-many group binding type:
    1. Every member of the binding (sending or receiving) will have at least one address table slot consumed by the group binding. Freeing up address table slots may require some creative manipulation of the bindings. Options are:
      • Convert to one-to-one bindings where the receiving controller will not lose an address table slot
      • Do not customize every individual combination of group bindings (i.e. send the setpoint to the same controllers that are receiving outside air temp, even if they won't be using it). Every unique combination of controllers will constitute a new group and thus consume a new address table slot in each controller.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 3903
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of