I/NET Security Control Unit (SCU) firmware releases

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET Security Control Unit (SCU) firmware releases
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • ScottLeedberg
    ScottLeedberg
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2570 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET Security Control Unit (SCU) firmware releases

Picard Product_Support
‎2018-09-11 07:03 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:46 PM

Issue

  • Should we upgrade to the latest revision for the SCU 1284
  • If we do not upgrade the SCU will I/NET work properly.

Product Line

TAC I/NET

Environment

  • I/NET Seven
  • Security Control Unit (SCU) 1200 series firmware 3.2x and above

Cause

The recommendation is to always upgrade to the latest revision. In some cases this is not always possible. Please review the information below to determine if these features and fixes are required for your installation.

Resolution

I/NET Seven is backward compatible with all previous hardware firmware revisions of the SCU. The recommendation is to always upgrade to the latest revision to enable all of I/NET's features and fixes included in these revisions. In some cases this is not always possible. Please review the information below to determine if these features and fixes are required for your installation.

If you have any additional concerns then please contact Product Support.

The following table lists the release firmware revisions and associated fixes and new features:

Rev Date DCN Changes
3.21 05/06 5593 Add support for SCU tamper to the SCU1200 and SCU1280
3.22 01/07 5610 Start adding intrusion alarm support to SCUs
Add issue level support to SCU1284
Fix defect where deleting last tenant from DPU causes incorrect schedules
Add door code
3.23 08/07 5627 Fix defect where changing a door to "unselect" did not prevent access through door
3.24 10/07 5631 Expand individual count from 24,000 to 32,000 per tenant
3.25 07/08 5657 Implement various changes to intrusion alarm system that were identified during EN50131 certification
3.26 01/10 5677 Fix corrupt reader LED due to OP5 monitoring board
Fixes to SCU1284 expansion board for IAS power monitoring
3.27 07/11 5717 Make AMT show person who commanded PIN functions
3.28 12/12 5739 Fix for bad card read on reader number 4 with internal AO at bit offset 04
3.29 08/13 5745 Fix so that a change of date from one month to the next will work correctly when using special days
3.30 10/14   Support for 130-bit Wiegand card
New event named “Key reassignment”
3.31 12/14 5754 Support for 86-bit Wiegand card

For DPU range of controllers refer to I/NET Door Processing Unit (DPU) 7910A / 7920A EPROM Feature matrix.

Labels (1)
Labels:
  • TAC INET
Tags (2)
  • Find more articles tagged with:
  • 15806
  • matrix
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore