How to remove data for all logs prior to a specific date in a Niagara R2 Enterprise Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to remove data for all logs prior to a specific date in a Niagara R2 Enterprise Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2677 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to remove data for all logs prior to a specific date in a Niagara R2 Enterprise Server

Picard Product_Support
‎2018-09-07 03:11 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:45 AM

Issue

How to remove, from a Niagara R2 Enterprise Server station, data for all logs prior to a specific date with one command.

Product Line

TAC IA Series

Environment

I/A Series R2 Enterprise Server

Cause

Cloudscape database management

Resolution

There is a utility that will allow deleting of records before a certain date of all or specific tables in the cloudscape database. The space from deleted records can also be recovered after deleted. This utility is called CloudscapeAdmin and is downloadable from The Exchange Download Center.

Download cloudscapeAdmin.jar and place in the x:\niagara\[NiagaraRevision]\nre\lib directory (for Builds 431 and higher).

To run this utility the station will need to be stopped. Once the station is stopped, open the console from either the created short cut or x:\niagara\[NiagaraRevision]\nre\bin\console.exe. From here type ‘nre CloudscapeAdmin’ and hit enter to view the commands to use it. 

There are two functions that cloudscapeAdmin can do:

  1. Delete; The delete command deletes records before a certain date but does not reduce the size used on the disk. The empty area of the database will be filled with new archived data.
  2. Compact; The compact command deletes records before a certain date and recovers the space from the disk. This process is slower.

Command:
nre CloudscapeAdmin x:\niagara\[Niagara Revision]\stations\[Station Name] [User Name] [Password] [delete or compact] [tablename or all] [date]

Sample Delete commands:
nre CloudscapeAdmin c:\niagara\r2.301.522a\stations\StationName admin admin delete all 2007-07-01

Sample Compact commands:
nre CloudscapeAdmin c:\niagara\r2.301.522a\stations\StationName admin admin compact all 2007-07-01

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3347
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore