Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How to integrate I/NET with Pelco Analog Matrix

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to integrate I/NET with Pelco Analog Matrix
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • sesa145087_brid
    sesa145087_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5461 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to integrate I/NET with Pelco Analog Matrix

Picard Product_Support
‎2018-09-10 10:17 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:40 PM

Issue

How to integrate I/NET with Pelco Analog Matrix in order to implement some features, such as:

  • Switch specific camera image to specific monitor.
  • Switch specific camera to specific preset and display it on specific monitor.

Product Line

TAC INET

Environment

  • I/NET
  • Pelco CCTV system
  • Pelco Matrix

Cause

In some projects there is demand for access control system to integrate with analog CCTV system to do the alarm interaction. I/NET can integrate with Pelco CCTV system with ASCII code communication.

Resolution

I/NET communicates with Pelco analog CCTV system through ASCII code. There are two kinds of communication port for Pelco matrix, which are RS232 and RS485/422. For RS232 port for matrix, an RS232 to RS 232 cable is needed. If there are no COM ports for computer, an USB to RS232 converter is needed. For RS485/422 port for matrix, an RS232 to RS485/RS422 converter or USB to RS485/422 converter is needed. Connect the I/NET server to Pelco matrix through this converter, and the steps below should be followed:

  1. Open the I/O Configuration of I/NET, and choose the port for text output port and baud rate for the port communicating.


  2. In the AMT, choose Edit--->Text Library, and click Add.
  3. Choose a point for alarm interaction, and the status of the point to activate the interaction: alarm, acknowledge, return to normal (RTN) and acknowledged/return to normal (RTN).


  4. In the text area, enter the ASCII code for matrix. For the two applications of the alarm interaction, different ASCII code should used:
    • 1Ma1#a, which means switching 1# camera image to 1# monitor
    • 1Ma7#a1\\a, which means switching 7# camera to 1# preset and display it on 1# monitor. Here "\a" is an escape sequences for I/NET, so we need one more "\".

Then the integration with I/NET and Pelco CCTV system is finished. When the specific point goes into alarm, then the specific camera can be switched to specific preset and displayed on specific monitor.

For more applications of the integration with Pelco analog matrix, refer to the documentation for the Pelco ASCII Protocol Manual.

And for more information about how to set text output in I/NET, refer to Text Output through RS-232 Port in I/NET.

Labels (1)
Labels:
  • TAC INET
Attachments
Tags (2)
  • Find more articles tagged with:
  • 8344
  • inet
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore