Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

General Information on RS-485 Communication

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • General Information on RS-485 Communication
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • AdamSteele
    AdamSteele
  • AbeMeran
    AbeMeran
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
4445 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

General Information on RS-485 Communication

Picard Product_Support
‎2018-09-11 06:47 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 07:00 PM

Issue

General questions and best practices for RS-485 protocol including cable length and terminating resistors

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

MSTP

Cause

Understanding best practices for installing, cabling, and terminating RS-485 networks can avoid a lot of problems with communication and hours of troubleshooting communication problems.

Resolution

MS/TP

MS/TP stands for Master Slave Token Passing. Each device on the link is considered the master when it has the token. If it does not have immediate need to use the token, it is required to pass the token along to the next device. This is the token passing part. All devices on the link which do not currently have the token are regarded as slaves, and are expected to listen to any messages the current master may have for it. Because all devices take turns being master, the link is effectively peer to peer.

Electrically, MS/TP adheres to standard RS-485, physically wired using two-conductor shielded twisted pair cable.

RS-485 Cable Specifications

Cables used to form the RS-485 network should conform to the following specifications:

Wire Size: 22-24 AWG
Cable Type: Twisted-pair, copper wire, tinned
Shield: Braid
Nominal Impedance: 100-120
Velocity of propagation: 78%
Capacitance: <12.5 pF/ft between conductors and <22 pF/ft between the conductor connected to ground and the next conductor.

Topology

Daisy chain bus topology.

Star topology can be achieved using Infilink/B-Link repeaters.

Maximum Cable Length

Cable lengths of up to 4000 ft (1220m) daisy chained from controller to controller on one arm of a star are supported. After 4000 ft (1220m), a signal repeater (b-Link) is required to add more nodes to the network or further extend the cabling. Using a b-Link fiber repeater allows you to extend the length of RS-485 with fiber optic cable, recommended for running cable between buildings and through noisy environments.

Maximum Number of Devices

TAC's MS/TP RS-485 supports a maximum of 127 nodes overall. Each controller represents a single node on the network.

RS-485 Termination

The MS/TP field bus requires a 120 ohm terminator resistor at both ends of a daisy chain segment. The following diagram illustrates the connection of the terminator:

Also check out the SmartStruxure-RS485-Network Installation Quick-Help video on the Exchange.

Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 15518
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore