Field bus (Infinet or MSTP) will shut down as soon as device is connected

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Field bus (Infinet or MSTP) will shut down as soon as device is connected
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2333 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Field bus (Infinet or MSTP) will shut down as soon as device is connected

Picard Product_Support
‎2018-09-11 06:27 AM

Last Updated: Administrator CraigEl Administrator ‎2025-07-06 06:21 PM

Issue

Infinet/MSTP was running fine until a device was added or replaced, after wiring in the new device it brings down the Infinet/MSTP field bus when powered up, disconnecting the new device from the bus makes the bus resume operation.

When the new device is connected the green (RD) LED goes solid instead of blinking and all communications to all devices on the bus stops, in some cases the master controller will reset.

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

  • Infinet devices
  • i2s
  • MSTP devices
  • b3s

Cause

Power lines reversed. Continuum field devices (i1s, i2s and b3s) have their RS-485 communication lines connected to ground via an isolator as seen in the diagram below, if the LIVE and GND lines are inverted then LIVE is connected to the 485 communication lines instead of GND.

This will make the field bus electrically unable to communicate and, in some scenarios, can even cause hardware damage.

Resolution

Ensure Correct Wiring:

  • When powering 24VAC devices off the same transformer, make sure to continue the wiring chain LIVE to LIVE and GND to GND.
  • In the field, it may not be very obvious that the 'Live' and 'GND/Neutral' wires have been swapped. A multi-meter can be used to verify the wiring.
    1. Set the multi-meter as appropriate to measure 24VAC.
    2. Place the black lead of the meter on the GND/Neutral termination at the power connector of the field device. 
    3. Use the red lead of the meter to measure the voltage at the +/- termination at the RS-485 (Infinet or MSTP) on the controller.
    4. The measured voltage should be very low, between 0 VAC and 1.1 VAC, a voltage reading of about 10 VAC indicates the Live and GND/Neutral wires have been swapped.
Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 15151
  • AbeMeran25
  • offline
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore