Energy Reports not working in 1.3 and earlier
  • Energy Reports not working in 1.3 and earlier
  • Cody_Failinger
    Cody_Failinger
  • Derrick_Ratliff
    Derrick_Ratliff
  • RobertAndriolo
    RobertAndriolo
‎2018-09-10 11:13 PM
  • StruxureWare Web Reports
  • StruxureWare Reports Server
For 1.3 and earlier, in order for a log to be tracked as an energy report it must have a units type that indicates it is a metered signal.
For any logs that do not have Units set.  Add one of the possible Unit types shown below.
You should not change units on a log that is already running.  If you have entered the wrong type of units you will need to delete and re-create the logs. If this is not possible.  Use the following directions:
  1. In the System tree pane, browse to System>Report manager
  2. View the metering log filter property to see all unit types that will be interpreted as Energy logs.  The energy objects must all reside within a single Energy folder.
  3. In the event that you have already set unit on a log, you should be able to add the unit to the list in this field.
Note:  It is not necessary to include the prefix / suffix of the same unit.  That is if you are using MWh or kWh then this is covered by the unit Wh in the Meter log filter.  You must make sure that the units are defined in the monitor point (object), trend log and associated extended trend log for the values to be shown in the Energy Reports.
  • 12055