Default IP address following Xenta Server "format" command is different than from factory
  • Default IP address following Xenta Server "format" command is different than from factory
  • HenrikTarpgaard
    HenrikTarpgaard
  • Benji
    Benji
  • CraigEl
    CraigEl
‎2018-09-07 01:58 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:24 PM
The Xenta 7xx from factory it has the default IP address 192.168.255.2, which also is stated in the manual. But when you run the “format” command on a Xenta 7XX, you will get IP address 172.22.1.5.
Satchwell MicroNet, TAC INET, TAC Vista
  • Xenta Servers
  • Xenta 511, 527, 527 NPR, 555, 701, 711, 721, 731, 901, 911, 913
The format command will wipe all memory from the Xenta Server. Its IP address will need to be reset, system program will need to be reloaded, and XBuilder project will need to be redownloaded.
  • The Xenta from factory has the default IP address 192.168.255.2 subnet mask 255.255.255.0
  • After the “format” command it will have IP address 172.22.1.5 subnet mask 255.255.255.0
See IP setup for a Xenta server (Xenta 5/7/9xx) through serial communication for instructions on setting the IP address to the desired address.