Posted: 2021-06-03 01:46 PM
Hello,
Could you please give me guidance to size SP90 network?
Best regards
Espé
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-03 07:53 PM
This probably depends on whether Modbus or BACnet is being used. Since it doesn't state the unit load of the device, it's best to assume a UL of 1 and therefore a maximum of 32 devices.
This is also noted on page 7 the Product Manual
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-03 07:53 PM
This probably depends on whether Modbus or BACnet is being used. Since it doesn't state the unit load of the device, it's best to assume a UL of 1 and therefore a maximum of 32 devices.
This is also noted on page 7 the Product Manual
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-04 05:43 PM
I've created a Knowledge Base article that provides further guidance on this.