TROUBLESHOOTING old modicon plc.

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • TROUBLESHOOTING old modicon plc.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Industry Automation and Control Forum
Start a Topic
Solved
Rishi1
Crewman Rishi1
Crewman

Posted: ‎2022-08-07 11:43 PM

0 Likes
1
4896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-07 11:43 PM

TROUBLESHOOTING old modicon plc.

I want to communicate and diagnose the fault appearing in the plc,through software.

Its modicon TSX premium.I Want to know

-   what is the setup required for communication

    which is the software,os,communication cable etc.

in my plc rack i have modules TSX PS7303A , TSX ETY4103 with this how can i connect with pc

- TSX PS7303A is having rs232 round pin i assume ,i dont have the cable.if i get the pinout i can make the cable myself.

-  TSX ETY4103  this module is having ethernet port but i dont know the ip address or how to establish communication.

please check the attached image for details

Attachments
modicon.rar
Labels
  • Labels:
  • Asset Performance
  • Connected Products
  • Edge Control
  • Hybrid DCS
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2022-08-08 12:18 AM

1 Like
0
4884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-08 12:18 AM

Hello Rishi,

 

1: This Modicon premium CPU is probably programmed with PL7. PL7 is no longer available for download since 2018 as it's in service mode. So you need someone who can provide you a copy. Could also be programmed with the current UnityPro/EcoStruxure Control Expert software, is this particular CPU type could be upgraded with new firmware. This is not shown by the Partnumber of the CPU, as this is a just a firmware upgrade. You need the application file or some other information from the owner showing this.

2: If you want to diagnose/debug the application you need a copy of the original application. If you're lucky you can upload this application form the CPU, but only if the original program was transferred including the upload information. If this was transferred without upload information, you need the original application file.

3: The TER port is an RS485 port. Easiest to use this, is using the original cable which includes an RS232/RS485 converter. Do not start building your own. Also these cable sets are no longer available for sales.

4: Connect to the ethernet port on the TSXETY4103 module. If you do not know the IP address (available in the original application file) you can try to connect your laptop to the Ethernet port and use WIRESHARK (free download). At powerup, the ETY module will send some "Gratious ARP" messages showing it's IP address.

5: You need to install XWAY drivers (part of PL7 programming package) to communicate with the CPU through Ethernet and through the TER port.

 

My advice:  Find someone who has experience and the (application) software, or ask your local Schneider Electric service organization.

 

R.Roozee
Sr Solution Architect (SAE Master)

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2022-08-08 12:18 AM

1 Like
0
4885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-08 12:18 AM

Hello Rishi,

 

1: This Modicon premium CPU is probably programmed with PL7. PL7 is no longer available for download since 2018 as it's in service mode. So you need someone who can provide you a copy. Could also be programmed with the current UnityPro/EcoStruxure Control Expert software, is this particular CPU type could be upgraded with new firmware. This is not shown by the Partnumber of the CPU, as this is a just a firmware upgrade. You need the application file or some other information from the owner showing this.

2: If you want to diagnose/debug the application you need a copy of the original application. If you're lucky you can upload this application form the CPU, but only if the original program was transferred including the upload information. If this was transferred without upload information, you need the original application file.

3: The TER port is an RS485 port. Easiest to use this, is using the original cable which includes an RS232/RS485 converter. Do not start building your own. Also these cable sets are no longer available for sales.

4: Connect to the ethernet port on the TSXETY4103 module. If you do not know the IP address (available in the original application file) you can try to connect your laptop to the Ethernet port and use WIRESHARK (free download). At powerup, the ETY module will send some "Gratious ARP" messages showing it's IP address.

5: You need to install XWAY drivers (part of PL7 programming package) to communicate with the CPU through Ethernet and through the TER port.

 

My advice:  Find someone who has experience and the (application) software, or ask your local Schneider Electric service organization.

 

R.Roozee
Sr Solution Architect (SAE Master)
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore