Hello,
I setup an ATV 320 V.F.D. in IO profile mode,
as I started the motor I receive status word from V.F.D. :
Ready to switch, Ready to operate and error.
While the motor is running we get Boolean state "FALSE" on signals as if V.F.D. is not ready to switch and it is not ready to operate.
We don't get error information, V.F.D. just stops the motor and waits for the next command.Ready to switch and ready to operate signals stay FALSE until i reset "RUN" bit in command word. After that they go back to state "TRUE".
This all happens in process where we simply want to run our motor constantly without turning off, and we don't have any idea why would it suddenly in the running state stop being ready and waiting for next command as if his command is always be running..
Could anyone help me with this one?
Thank You
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-08 09:59 PM
Are you sending command through modbus from PLC?
if yes, make sure this command always send periodically. if it doesn't, VSD will back to ready state for safety reason.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-10 12:58 AM
Hello,
There is a communication control on Modbus, the ATV controls that there are requests sent periodically. Normally if you read the status of the ATV periodically, it is enough to maintain the control of the communication.
Here after an extract from the documentation:
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-14 12:25 AM . Last Modified: 2020-02-14 12:38 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-14 12:25 AM . Last Modified: 2020-02-14 12:38 AM
Hello, thank You for your reply,
I am sending the command word via Profinet every communication cycle. The drive is fitted with VW3A3627 module. 2 out of 14 drives are the only ones to have this problem.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-18 01:04 AM . Last Modified: 2020-02-18 01:06 AM
@Anonymous user
you can try to switch over the 2 VSD IP address with a good one.
if the problem appear on new IP (old VSD) the source of problem could be on VSD configuration.
if the problem appear on old IP, then your problem could be on your PLC setting/program.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-18 01:15 AM
Do all of the drives have identical configurations? (the answer to this should of course be 'no', since they likely have different motors / different node addresses)
But importantly, is the SLL [Modus fault Mgt] field set to 'no' on ALL of the drives?
Make sure that safety is afforded in a more robust manner than just using this setting of course.. otherwise death may occur.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-23 12:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-23 12:21 PM
@Anonymous user
Hii veki, i just done my proheject controling atv12 via modbus using hmi gxu3511, if you communicate direct without PLC, make sure the reference channal and command channel in right configuration example 'reference channel is set to modbus (ndb)' and command channel (cd1) is set to ndb, you must set the value is in special addres in my case is 8502(reference freq) and 8501(command channel) set 6, 7, 15( to run the drive ) refers to modbus communication manuals, atv320 communication parameter
(excel file )
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-23 12:22 PM
And if using plc make sure that plc have special flag clock