Posted: 2024-12-03 09:07 PM
Hello Juan Rayo,
Hope you are doign good !!...
CPU866e - EB V1.7.30 - AI8AO4 module AO configured as Voltage (0/5V) or Current (4/20mA) but we are not getting the output in field TB.
As per AI8AO4 user manual It was observed that there is some jumper setting for Voltage/Current configuration, but in newly supplied AI8AO4 modules (PN- M525200002E6, SN- 2441R1511239 )internal PCB there is no Jumper settings.
Pictures enclosed for your quick reference. AO Wiring, AO_TB we are using at your panel pic enclosed.
New AI8AO4 PCB picture also enclosed.
Can you suggest How to check the AO signals?
Regards,
Amarnadh P
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-04 03:01 AM
Definitely the document is wrong in terms of jumpers needed. The module only works with current as default BUT if you want to work with voltage you must add resistances in the fieldTB and then select the correct working voltage level depending on the resistance´s value added. We start working to correct the document, thanks for the feedback
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-04 07:47 AM
Thank You for your support!!
There was Hardware issue. We have replace with new one. Now it is working.
Regards,
Amarnadh p