Dear All,
is there anyone can help me ?
i want to use M221 as Modbus Serial Gateway
is it possible ?
and how to do it ? because i'm not succeed yet
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-11-25 10:31 AM
Hi,
The M221 PLC has one RS-485 Modbus port. Using this port, you can read data from Modbus slave devices and assign the values you read to the internal registers of the TM221.
In the system, a client can also treat the TM221’s Ethernet port as if it were a slave (server) device, and the TM221 will serve its own registers to that client.
However, to do this, you need to write a small amount of code as described above.
It cannot be used as a gateway with only configuration settings like a typical off-the-shelf gateway device. Still, it can function like a gateway as long as the system requirements and limitations are taken into account.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-11-25 10:20 PM
Dear @ismailozinan
Thank you for your info,
but i still cannot actually succeed to pull data from my field device
this is the screenshot
is there anything wrong with it ?
can you help me ?