ATV630D18N4 Firmware update failure

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • ATV630D18N4 Firmware update failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
Start a Topic
tiago_angelo
Crewman tiago_angelo
Crewman

Posted: ‎2024-05-16 11:32 AM

0 Likes
8
2404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-16 11:32 AM

ATV630D18N4 Firmware update failure

Good evening, I have an ATV630D18N4 and decided to update its firmware..

Original firmware is/was 2.5IE30B10, target is the latest version from Schneider 3.8IE42B05, I'm already using the latest version of Automation Device Maintenance and added the two certificates that are referred here:

https://www.se.com/ie/en/faqs/FAQ000256127/

 

I'm connected over Ethernet.

 

On the logs I get this:

5/16/2024 7:13:18 PM Opened connection to device [10.50.4.101]

 

5/16/2024 7:14:24 PM Starting firmware download
5/16/2024 7:14:24 PM Transferring firmware 0/72
5/16/2024 7:18:33 PM Transferring firmware 71/72
5/16/2024 7:18:33 PM Firmware transfer complete: Disconnect success
5/16/2024 7:18:33 PM Applying firmware update, please wait a few minutes
5/16/2024 7:18:33 PM Firmware transfer complete: Disconnect success
5/16/2024 7:18:33 PM Do not press any key on the display terminal, until the Apply operation is completed
5/16/2024 7:18:36 PM Firmware update status changed: SAVE >> 36
5/16/2024 7:18:36 PM Firmware update is ongoing
5/16/2024 7:18:36 PM Do not press any key on the display terminal, until the Apply operation is completed
5/16/2024 7:18:45 PM Firmware update status changed: PROG >> 36
5/16/2024 7:18:45 PM Do not press any key on the display terminal, until the Apply operation is completed
5/16/2024 7:18:45 PM Firmware update application failed
5/16/2024 7:18:45 PM Load sequence failed with message (5) ERROR_OPERATION_FAILED (Message: )
 
I have already power cycled the drive, but its now stuck in the failed firmware update error.

What can I do, is it possible to have the original firmware files and try to flash them instead?

 

Best regards.

 

 

 

 

 

 

 

Labels
  • Labels:
  • Process Automation Talks
  • Tags:
  • ATV630
  • english
  • firmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2024-05-26 11:49 PM

2 Likes
3
2348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-26 11:49 PM

Hi I have forwarded per E-Mail an invintation to a onedrive link were you could find all FW Versions.

So far I see you need first to update to an earlier version then v3.8. But I´m not a specialist in this topic. Please contact your local Level 2 support. I would expect they could support you by this topic.

Reply

Link copied. Please paste this link to share this article on your social media post.

tiago_angelo
Crewman tiago_angelo
Crewman

Posted: ‎2024-05-27 08:29 AM

1 Like
2
2334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-27 08:29 AM

Thanks Bastian_Schmitz.

 

I will try an older version of the firmware, if I can't solve it I will contact my local Schneider support.

 

Best regards!

Reply

Link copied. Please paste this link to share this article on your social media post.

Hammer
Hammer Cadet
Cadet

Posted: ‎2024-06-26 09:23 PM

In response to tiago_angelo
0 Likes
1
2270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-26 09:23 PM

Hi.
I encountered the same problem now. 🙂
How did you solve it?

Reply

Link copied. Please paste this link to share this article on your social media post.

CB1
CB1 Cadet
Cadet

Posted: ‎2024-12-18 11:48 AM

In response to Bastian_Schmitz
0 Likes
0
1780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-18 11:48 AM

Hi Bastian ,

I am also now stuck in the failed firmware update error.

What can I do, is it possible to have the original firmware files and try to flash them instead?  Could you send me the old FW versions also.   Also how do I contact "Local Level 2 Support?" Thanks

 

Reply

Link copied. Please paste this link to share this article on your social media post.

CB1
CB1 Cadet
Cadet

Posted: ‎2024-12-18 11:49 AM

In response to Hammer
0 Likes
0
1780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-18 11:49 AM

Were you ever able to get out of the firmware update , if so how?   Thanks

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Bosswaffle
Lt. Commander Bosswaffle
Lt. Commander

Posted: ‎2025-01-14 04:52 PM

In response to Bastian_Schmitz
0 Likes
0
1545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-14 04:52 PM

@Bastian_Schmitz Could I get a link to all of the current firmware for ATV630U75N drives? I have 2 drives stuck at 3.7, and I'm trying to upgrade to 4.1

Reply

Link copied. Please paste this link to share this article on your social media post.

Jacob_AET
Jacob_AET
Cadet

Posted: ‎2025-11-25 05:42 PM

In response to Bastian_Schmitz
0 Likes
0
214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-25 05:42 PM

Hi Bastian,

Can i please get a copy of the link to al the FW.
Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2025-11-26 02:10 AM

0 Likes
0
207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-26 02:10 AM

He please donwloaded this tool LINK 

And then contact your local Support. They could forward the Firmware file. Not any firmware is compatible to any Hardware revision of the drive. But the local support should have the visibility

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore