TM172PDG28SI (Ethernet port randomly turn to offline)
Dear developers,
There are about 10 PLCs (TM172PDG28SI). All of them connected to switch (BMS network) via ethernet (ModBus-TCP).
Randomly some of ports turn to offline.
But!!! After reconnecting (off/on) RG45 connector, - PLC turn to online with absolute guarantee.
So,
1) Length between each one PLC and switch less, than 50 m
2) Every of PLCs connected to switch with FTP cable
2) There is a plastic RJ45 connector at PLC side
3) There is a metal RJ45 connector at switch side
4) Switch is connected to the PE
!Also I had been trying to use the metal rj45 connector at both sides, but result is the same
Is anybody have an experience for solute my problem.
May be there are some system words or system bits at the PLC level, that's can to provide some extension information about ethernet port
BR
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-11 12:37 AM
1. Firmware version is 596.9
2. Static IPs
3. for now sysMbSTcp_SocketServerinfo is not implement in PLC application, so as soon as possible I'll download PLC application with sysMbSTcp_SocketServerinfo, and when PLC will turned to off, I'll try to monitor return value via the RS-485 interface. But I'm absolutely sure, that PLC has another behavior at socket overflow - it is not accessible via ModBus TCP, but it has the IP ping. In my case, PLC has no any ping, but after RJ45 reconnecting, the ping is restore
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-13 03:39 AM
It's most likely that it's the switch being responsible for the 'port down' action, so you should be able to look in the logs for the switches.
If you have lots of PLCs, and a cheap unmanaged switch, then it's possible that the large number of small packets/frames from the PLC communications is overwhelming the switch processing (if it's not able to offload at line rate).
I've definitely seen this behaviour on older 10/100Mbps switches, where whilst they could handle 1x 100Mbps stream, when given 16x 100Mbps aggregate traffic from thousands of frames per second (i.e. like 200 bytes per frame) they just locked up ports, and then rebooted the PHYs (obviously they got too confused).