Posted: 2025-09-08 07:14 AM
There are very different types of temperature sensors listed on the hardware guide for TM172.
Two questions:
1) what is the criteria to select NTC or PT1000 ? Range is the same for both types.
2) depending on the beta values, the input configuration should be selected accordingly. I have not been able to find which beta value corresponds to the TM1ST sensors (I have used Cfg_Aix = 0 before). Is that ok ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-08 10:06 PM
All NTC Sensors in the SE offer are Beta 3435 (=2).
The NTC Sensor Beta 3977 (=0) is only available as Eliwell product.
This type is normaly used as compressor discharge temperature probe.
The "normal" NTC (=2) could not measuer such high temperatures, he stopped at ~120°C.
The PTC sensor is also not available as SE product, and the full type is KTY81-121
The Sensors of the SE Building portfolio has different beta values and could be used with additional librarys.
I prefere to use the NTC probe. This sensor is together with the M17x PLCs more accurat then a PT1000 probe. And the NTC sensors are less cost intensive. The PT1000 function is usefull if you need for your application a special sensor which will be manufractured from a third party supply. In that case everbody understand a PT1000 element, but not everybody could deliver the needed NTC probe with the correct BETA value.
If you use the standart SE NTCs, and configure them as 0 you will always get problems with the accuracy. An offset will only work at one fixed point. That is the reason why the AI configuration use as standard 2 and not 0.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-08 10:06 PM
All NTC Sensors in the SE offer are Beta 3435 (=2).
The NTC Sensor Beta 3977 (=0) is only available as Eliwell product.
This type is normaly used as compressor discharge temperature probe.
The "normal" NTC (=2) could not measuer such high temperatures, he stopped at ~120°C.
The PTC sensor is also not available as SE product, and the full type is KTY81-121
The Sensors of the SE Building portfolio has different beta values and could be used with additional librarys.
I prefere to use the NTC probe. This sensor is together with the M17x PLCs more accurat then a PT1000 probe. And the NTC sensors are less cost intensive. The PT1000 function is usefull if you need for your application a special sensor which will be manufractured from a third party supply. In that case everbody understand a PT1000 element, but not everybody could deliver the needed NTC probe with the correct BETA value.
If you use the standart SE NTCs, and configure them as 0 you will always get problems with the accuracy. An offset will only work at one fixed point. That is the reason why the AI configuration use as standard 2 and not 0.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-10 04:00 AM
Thanks for your detailed explanation. I wrote "Cfg_Aix = 0" but actually I did so from memory. I have been using the default value so far which is Cfg_Aix = 2, so I am on the safe side.
We did buy some PT1000 TM1STPTTSN52050 once which are on our warehouse. From your answer I will go ahead and use them.