Posted: 2023-02-14 08:32 AM
M172 HMI message pop-up
I am trying to make alarms visible on a "pop-up" screen in M172 HMI. I do it by using a "Message" instead of a regular page. An example code is available here .
I define a couple of status variables to do this and use them in a GlobalOnTimer procedure. ActiveAlarm is ON whenever at least one alarm is active, and AlarmIgnore is used to tell the PLC to stop sending alarms for some time:
//ActiveAlarm : at least one alarm is active
uiret:=Video_GetParam(0,Addr_ActiveAlarm,0,?ActiveAlarm,tyBool); // See if alarms are active
//AlarmIgnore : tell the PLC not to cycle alarms
uiret:=Video_GetParam(0,Addr_AlarmIgnore,0,?IgnoreAlarm,tyBool); // See if alarms are acknowledged
//Alarm Pop Up screen
IF ActiveAlarm THEN
IF NOT AcknowledgeAlarm THEN
msg_id_opened:=1; //Make sure what page number is loaded
uiret:=Video_SendEvent(kWM_MSG,msg_id_opened);
END_IF;
ELSE
IF HMI_usiPosition = 1 THEN
msg_id_opened:=0;
uiret:=Video_SendEvent(kWM_KEY,kKEY_VK_F3); //Close pop up
//Define global virtual key VK_F3 as close
END_IF;
AcknowledgeAlarm := FALSE;
END_IF;
There´s a couple of minor corrections needed but the code works both in simulation and on a physical target (TM172PDG18R), as long as I connect to the target and "Download all" the project.
However, if I need to correct the HMI code or screens, I can connect to the PLC but when I finish the process of downloading the new HMI code, PLC hangs and I get either WDT3 or HMI can not be loaded error when the PLC starts.
So, the problem lies on the GlobalOnTimer procedure. If I remove the Video_SendEvent function and open the screen with a button instead, there are no issues.
Any comments on how to improve this will be welcome.
- Labels:
-
HVAC
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-14 08:37 AM . Last Modified: 2023-02-14 08:38 AM
Hi,
So far I remember exactly for this purpose is the Target function sysHMI_Message in Programming integrated.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-14 09:26 AM
Thanks Bastian for the tip.
Do you remember if there´s anyway to close the popup from programming ? I tried setting the input to a not valid value but it does not close it. Or do I need to write an OnTimer procedure in the message screen ?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-17 02:13 PM
Hi,
the limit of sysHmi_Message() is that it works only on local display and not on the remote TM17xDGRP.
The reason of the watchdog I think is that the code tries to open infinite time the popup.
I haven't tested it, but try to modify the code more or less in this way:
GLOBAL TIMER SCRIPT:
//ActiveAlarm : at least one alarm is active
uiret:=Video_GetParam(0,Addr_ActiveAlarm,0,?ActiveAlarm,tyBool); // See if alarms are active
//AlarmIgnore : tell the PLC not to cycle alarms
uiret:=Video_GetParam(0,Addr_AlarmIgnore,0,?IgnoreAlarm,tyBool); // See if alarms are acknowledged
//Alarm Pop Up screen
IF ActiveAlarm THEN
IF NOT AcknowledgeAlarm AND NOT(xMsg1Open) THEN
msg_id_opened:=1; //Make sure what page number is loaded
xMsg1Open:=TRUE;
uiret:=Video_SendEvent(kWM_MSG,msg_id_opened);
END_IF;
ELSE
AcknowledgeAlarm := FALSE;
END_IF;
ONTIMER SCRIPT of the Message:
IF NOT(ActiveAlarm) THEN
xMsg1Open:=FALSE;
uiret:=Video_SendEvent(kWM_KEY,kKEY_VK_F3); //Close pop up
END_IF;
Close button of the Message must call the same script linked to OnTimer
Link copied. Please paste this link to share this article on your social media post.