Posted: 2023-01-26 01:01 AM
Hello,
I am having difficulties implementing TeSys U motor starter with safety PLC to ensure that no motor actuation is possible in case of a E-stop activation. I considered cutting coil COM with safety signal, but I am not sure if this is considered Safe. From design documentation it seemed to me, that this is easily achieved when using a hybrid starter, but no clear example is provided for all in one motor starter in documentation. In example provided below -K80.1 is controlled with safety output.
Example 1.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-14 11:14 PM
The question is which safety level you want to reach. A Hybrid starter Tesys H has in my opinion always a higher safery level then one Tesys Ultra. So far I understand in a Tesys H are two contacts in row. If you want reach the same with Tesys U you need one Tesys U and and one Tesys D. But at first you need to check which safety level is needed regarding to your risk assessment.
Disclaimer: I´m not a safety specialist