Checklist to deploy EcoStruxure IT Gateway

Get started with EcoStruxure IT

Everything you need to get started with EcoStruxure IT. Create an account, install the EcoStruxure IT Gateway, and download the mobile app.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Resources
  • Get started with EcoStruxure IT
  • Checklist to deploy EcoStruxure IT Gateway
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Demo available: IT Expert and EcoStruxure IT app
  • Checklist to deploy EcoStruxure IT Gateway
  • Notifications on the EcoStruxure IT website
  • Demo available: IT Expert and EcoStruxure IT app
  • Checklist to deploy EcoStruxure IT Gateway
  • Notifications on the EcoStruxure IT website

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Get started with EcoStruxure IT
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
24287 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Checklist to deploy EcoStruxure IT Gateway

Picard EcoStruxureIT
‎2019-04-04 07:13 AM

Last Updated: Sisko JLehr Sisko ‎2025-10-20 11:12 AM

 

This checklist will help you make sure you have the necessary information to deploy the EcoStruxure IT Gateway and discover devices successfully.

Installing and setting up the EcoStruxure IT Gateway - version 1.10 and newer

 

 

 

Server or VM

GW_checkbox_4428097906333.pngGW_checkbox_4428097906333.png

Server or VM to download and install EcoStruxure IT Gateway on.

Not applicable for the EcoStruxure IT Gateway appliance, which comes with the Gateway software preinstalled.

System requirements

 

Device IP addresses

You can import a device list in .CSV or .TXT format.

You can include SNMPv1, SNMPv3, NetBotz, and Redfish devices in one list. You import a list of Modbus devices separately.

GW_checkbox_4428097906333.pngGW_checkbox_4428097906333.png

List of IP addresses, IP address ranges, or subnets to discover devices on.

 

File transfer credentials - FTP and/or SCP

GW_checkbox_4428097906333.pngGW_checkbox_4428097906333.png

Username _________________

Password __________________

Port ____________

 

Device credentials

GW_checkbox_4428097906333.pngGW_checkbox_4428097906333.png

SNMPv1 enabled

 

Read community name (public is default) ___________________________

Write community name (private is default) __________________________

Port (161 is default) __________

GW_checkbox_4428097906333.pngGW_checkbox_4428097906333.png

SNMPv3 enabled

 

The small Gateway configuration can monitor up to 60 SNMPv3 devices total.

System requirements

EcoStruxure IT Gateway versions older than 1.15 do not allow discovery of SNMPv3 devices with the Authentication type or Encryption type set to None.

Note: When AES is configured on the APC NMC, choose AES128 in the Gateway.

Username ________________

Authentication type (MD5 or SHA) __________

Authentication password ________________

Encryption type (DES, DES3, AES128, AES192, AES256) ______________

Encryption password ________________

Port (161 is default) _____________

GW_checkbox_4428097906333.pngGW_checkbox_4428097906333.png

NetBotz

 

Username ____________________

Password _____________________

Port (80 is default, or 443 with SSL enabled) _____________

 

Web

Required to retrieve video clips from NetBotz 750/755 surveillance cameras

Username ____________________

Password _____________________

Port (443 is default) _____________

GW_checkbox_4428097906333.pngGW_checkbox_4428097906333.png

Redfish

 

Username _____________________

Password ______________________

Port (443 is default) ____________

GW_checkbox_4428097906333.pngGW_checkbox_4428097906333.png

Modbus

 

For each Modbus device to discover:

Device type ___________________

Device vendor _________________

Device family __________________

Server address ____________

For TCP:

IP address ____________________

Port (502 is default) _________

For serial:

Port _________

Baud rate _________

Data bits __________

Parity __________

Stop bits __________

Flow control __________

 

SSL certificate

If your organization operates an SSL inspection proxy and EcoStruxure IT Gateway does not trust the issuing CA, add the certificate authority's (CA) root certificate to the EcoStruxure IT Gateway trust store.

Your IT department can provide the correct root certificate.

The certificate must be in PEM format with one of the following extensions: cer, crt, or pem.

GW_checkbox_4428097906333.pngGW_checkbox_4428097906333.png

No certificate needed

GW_checkbox_4428097906333.pngGW_checkbox_4428097906333.png

Certificate file _______________________

 

Proxy server

The Gateway server must use the internet to communicate with EcoStruxure IT.

GW_checkbox_4428097906333.pngGW_checkbox_4428097906333.png

No proxy server needed

GW_checkbox_4428097906333.pngGW_checkbox_4428097906333.png

Proxy server

 

You can automatically detect the proxy server or configure settings manually.

Username _______________

Password ________________

Manual settings:

Proxy server address _________________

HTTP port __________________

HTTPS port __________________

 

 

Attachments
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore