Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Tag Bit addressing for the EtherNet/IP driver

Geo SCADA and Remote Operations Devices Ideas

Use this portal to submit your innovative ideas to make Geo SCADA Expert and Devices such as SCADAPack, Trio and Realflo of greater value to you and to the SCADA & Telemetry community. Every idea will be individually reviewed by our team for merit and will be marked Under Consideration.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Geo SCADA and Remote Operations Devices Ideas
  • Tag Bit addressing for the EtherNet/IP driver
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • SCADA 2
  • ViewX 2
  • Mimics 2
  • SCADAPack 2
  • Scripting 1
  • Virtual ViewX 1
  • Geo SCADA Expert 1
  • Efficiency 1
  • Configuration management 1
  • Modbus to WiStar 1
Idea Statuses
  • Submitted 7
  • Under consideration 133
  • Accepted 1
  • Declined 5
  • Partially delivered 0
  • Delivered 0
  • Abandoned 0
Related Products
Thumbnail of EcoStruxure™ Geo SCADA Expert
Schneider Electric
EcoStruxure™ Geo SCADA Expert
115
Thumbnail of SCADAPack 57x
Schneider Electric
SCADAPack 57x
2
Thumbnail of Accutech
Schneider Electric
Accutech
1
Load more
Completed Ideas
  • API driver

  • Accutech Modbus Master gateway to read Modbus devices and incorporate into WiStar net

  • Controller Key Enhancement

  • Restore "Embed Source Code for Upload" Option in Workbench (SP300 family)

  • DNP Outstation And DNP Master Diagnostics

View All
Top Liked Authors
User Likes Count
_Experimentalist_
Ensign _Experimentalist_
7
JonPGreen
Crewman JonPGreen
4
LStone_AA
Ensign LStone_AA
2
Hardin4019
Lieutenant Hardin4019
1
bmcneer
Ensign bmcneer
1
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
5 Likes

Tag Bit addressing for the EtherNet/IP driver

Status: Under consideration Submitted by Anonymous user on ‎2021-02-18 02:01 PM
5 Comments (5 New)

As per the email exchange with Amy Anger, it would be ideal to have the ability to access bits in the EtherNet/IP analog point tag field as possible in an OPC - Advanced analog point. 

This would allow for clients who use DINTs to package information in their systems fully transition to Geo SCADA smoothly. 

 

Tags (9)
  • Find more ideas tagged with:
  • Bit Address
  • DINT
  • english
  • ethernetip
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Comment

Link copied. Please paste this link to share this article on your social media post.

  • Back to Idea Exchange
  • Previous
  • Next
5 Comments
sbeadle
Kirk sbeadle Kirk
Kirk
‎2021-04-01 07:36 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-04-01 07:36 AM
Status changed to: Under consideration

Thank you.

du5tin
Lt. Commander du5tin
Lt. Commander
‎2021-04-30 08:23 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-04-30 08:23 AM

I wonder if this wasn't done because discretes are actually a BYTE coming across the protocol? 0=false, 255=true in the raw form? 

 

This was requested by several of our clients as well. Bit packing into DINTs is a super common practice. 

BevanWeiss
Spock BevanWeiss
Spock
‎2021-10-06 09:46 PM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-10-06 09:46 PM

I'd say that this should be implemented more in accordance with Modbus than OPC.

Modbus has a fixed 16 bit register (for IR / HR), requesting any bit reference within such a register is automatically promoted to retrieving the entire 16 bit register.

 

For PCCC / CIP when such a subindex is referenced, then it should be promoted (in the protocol side) to a full Item access, and then the subindexs split out as configured in Geo SCADA Expert 🙂

 

It might even be possible to re-use parts of this Modbus code... although in RSLogix world it's possible to apply subindexes on many data types.. DINTs, INTs, SINTs [I think... it's been a little while since I've tried this]

mohamedsheikhaleid
mohamedsheikhaleid
Cadet
‎2022-04-18 12:48 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2022-04-18 12:48 AM

GeoScada does not recognize the device's that deal with protocol ethernet/ip, I got files the extension(EDS) but I can't deal with them in geoscada.

field device abb circuit breaker e2.2n.

tanks you..

sbeadle
Kirk sbeadle Kirk
Kirk
‎2022-05-03 06:57 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2022-05-03 06:57 AM
Status changed to: Under consideration

Note:

You can use calculated points (triggered on Tag Processed) to work around this.

 

These expressions will work out bit numbers:

 

Bit 0: (".analog" mod 2)

Bit 1: (".analog" mod 4) >= 2

Bit 2: (".analog" mod 8 ) >= 4

Bit 3: (".analog" mod 16) >= 8

 

Etc.

Comment
Preview Exit Preview

never-displayed

Hint:
@ links to members, content
 
  • Back to Idea Exchange
  • Previous
  • Next
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore