Virtual ViewX Setup

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • Virtual ViewX Setup
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 11:40 AM
3 Likes
0
10970
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 11:40 AM

Virtual ViewX Setup

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 09, 2021 08:40 PM

📖 Home  Back  

Virtual ViewX Setup and Security Information

Virtual ViewX is part-OT and part-IT technology. Setup can be demanding particularly if the Windows server on which it is installed has been modified for some policies or settings specific to an end user environment. The guides below should help with security and troubleshooting.

 

Virtual ViewX Security

Virtual ViewX is configured by a combination of settings in the Virtual ViewX area and Internet Information Server (IIS). The following items are recommended:

 

Disable Legacy TLS within the IIS Web Server

You should disable older insecure TLS features within Virtual ViewX and the Geo SCADA Expert RP (Reverse Proxy). Find these web sites within the IIS Manager. For each one select Bindings near the top of the right-hand pane. Select the https binding and then select Edit.... Finally select the option Disable Legacy TLS.

 

Enable HSTS Within the IIS Web Server

HTTP Strict Transport Security (HSTS) is a widely supported standard that helps protect website visitors by ensuring that their browser always connects using an HTTPS connection. The certificate used to encrypt the session must be valid and trusted by the client.

The HSTS options can be found by navigating to the Geo SCADA reverse proxy website in IIS Manager and then clicking the HSTS link at the bottom of the right-hand pane. This will show a configuration dialog for enabling HSTS.

Customize the Virtual ViewX Web Headers

The web headers published to Virtual ViewX are used to control browser behavior, for example the ability to embed Virtual ViewX within other web pages. The headers are configurable within the file:

C:\Program Files\Schneider Electric\VirtualViewX\web-headers.json

 

To configure alternative options we recommend that you copy this file to:

C:\ProgramData\Cybele Software\Thinfinity\VirtualUI\web-headers.json

and make your changes. This will ensure that your customizations are not overwritten after a Virtual ViewX upgrade.

 

We recommend that the following lines are added/changed. Edit this line for "frame ancestors".

 

 

"frame-ancestors": "none",

 

 

 

And add this line under the item "X-XSS-Protection".

 

 

"X-Frame-Options": "deny",

 

 

 

Disable Autocomplete for the Login form

We recommend you disable automatic form completion for the login password. You can do this by changing an attribute in the login.html file. The file is located at C:\Program Files\Schneider Electric\VirtualViewX\web

Change:

 

 

 

<input type="password" name="password" id="password" value="" placeholder="Password" autofocus required autocomplete="password" />

 

 

 

To:

 

 

 

<input type="password" name="password" id="password" value="" placeholder="Password" autofocus required autocomplete="off" />

 

 

 

 

Make cookies secure through IIS Rewrite

When using Virtual ViewX on Windows Server, the HTTP web site on port 6580 (default) is made more secure using IIS on port 85 (default) and the Rewrite module. However, the HTTP port issues standard cookies but it is more secure if the Rewrite module changes these to secure cookies. Do this by editing the web.config file in the folder: C:\Program Files\Schneider Electric\ClearSCADA\RootHost

 

Insert these lines after </rules> and before </rewrite> (those lines included here).

 

 

 

            </rules>
            <outboundRules>
                <rule name="Ensure secure Cookies" preCondition="Missing secure cookie">
                    <match serverVariable="RESPONSE_Set_Cookie" pattern=".*" negate="false" />
                    <action type="Rewrite" value="{R:0}; secure" />
                </rule>
                <preConditions>
                    <preCondition name="Missing secure cookie">
                        <!-- Don't remove the first line here -->
                        <add input="{RESPONSE_Set_Cookie}" pattern="." />
                        <add input="{RESPONSE_Set_Cookie}" pattern="; secure" negate="true" />
                    </preCondition>
                </preConditions>
            </outboundRules>
        </rewrite>

 

 

 

 

 

 

 

What should I check if Virtual ViewX does not work?

The Geo SCADA Installation Guide, plus the Release Notes for Geo SCADA 2019 provide guides for setup, particularly when upgrading systems. It has advice to help you upgrade to Virtual ViewX.

 

We also provide the troubleshooting document attached to this article below:

Geo SCADA Virtual ViewX Troubleshooting Guide-xx.pdf

This document helps you with:

  • Setup
  • How it Works
  • Logging
  • Users and Security
  • Tips

If you need some help with getting Virtual ViewX working - and there are sometimes problems because Virtual ViewX is at the intersection of OT and IT, please read the above guide.

 

Latest changes: 28 Feb 2025. Version 1j. Added note on NLA, minor clarifications.

 

Notes on using INI files to log Virtual ViewX activity

Please use the latest set of INI files to specify log files. This is in the attachment below.

a) Delete existing logs in c:\Logs\*, or create folder if it does not exist.

b) Copy in just 3 files:

  • VirtualUISdk.ini and 
  • Thinfinity.VirtualUI.ini and
  • Thinfinity.VirtualUI.Server.ini to Program Files\Schneider Electric\VirtualViewX\bin32

c) Copy in ALL ini files to Program Files\Schneider Electric\VirtualViewX\bin64

d) Restart the ThinfinityVUISvcMgr service

e) Reproduce the issue

f) Delete only the INI files you added and then restart the ThinfinityVUISvcMgr service

This will reduce the chance that the logs are too large, and reduce the affect on performance and disk space by the logging.

It may be appropriate to enable browser traffic logging using the client browser's 'More Tools | Developer Tools' menu. Click the 'Network' menu, then toolbar item 'Clear Network Log' before the test, then click the toolbar item 'Export HAR...' when the test has completed.

 

Virtual ViewX and Single Sign-On

Geo SCADA uses the AVEVA Systems Management Server software and its AVEVA Identity Management features to provide Single Sign-on for ViewX (from Geo SCADA Expert 2023) and Single Sign-on for Virtual ViewX (from Geo SCADA Expert 2023, Update March 2024, further updates in November 2024).

The attached document Geo SCADA VVX and SSO Setup Guide Vxx.pdf is a worked example sequence of setup screens which may help you when setting it up.

VUILogs v11.zip
Labels:
  • Setup

  • ViewX

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore