| Property | Internal Point | Database Variable | Parameter | Comment |
|---|---|---|---|---|
| Database icon | Dark Grey | Yellow | Light Grey | |
| Which data steam are the values stored within? | Data stream | Data stream | Config stream | The choice of which steam is important should you export/import the object via SDE. SDE files only contain the config stream so on import the internal point and database variable will have no value |
| Permission required to change value | Control | Control | Configure | Generally operators will have the Control permissions but not Configure, this can be used to control who can change the value |
| Alarms | Analogue and digital: Yes String and Time: No | No | No | |
| Historic | Analogue and digital: Yes String and Time: No | No | No | |
| Value change logging | Standard event logging | Standard event logging | Config Changes table, if enabled | |
| Includes in count for licensing? | Yes | No | No | |
| Included data types | Analogue digital string time | Lots, including (array for some): Boolean, byte colour (RGB) double floats strings time variants | Postal address double grid reference object link parameter table string | |
| Triggers logic on-input changed | Analogue and digital: Yes String and Time: No | No | No |