Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

memory LINK150 (or EGX150)

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Re: memory LINK150 (or EGX150)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Romain_Polette Champion
128
Guillaume_Evrard
Guillaume_Evrard Leader
60
Randi_Dolan
Randi_Dolan Leader
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
sesa379798
sesa379798 Leader
Leader

Posted: ‎2016-02-24 02:01 PM

0 Likes
7
3110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-24 02:01 PM

memory LINK150 (or EGX150)

information about memory LINK150 (or EGX150) additional manual

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Kamal
Kamal Troubleshooter
Troubleshooter

Posted: ‎2016-03-07 10:46 PM . Last Modified: ‎2025-04-09 04:53 AM

2 Likes
2
2958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-07 10:46 PM

Hi Adrian,

Please find the answer

- What is the filesystem size/free space ? : Flash - 128 MB (total), used around (10 MB)

- What is the size of Ethernet Physical port 1 Reception/Transmission Buffer?   : On Application side we support - 32 (tcp connection) * 32 (serial packet ) * 255 bytes of memory.

- What is the size of Ethernet Physical port 2 Reception/Transmission Buffer?  : 32 (tcp connection) * 32 (serial packet ) * 255 bytes of memory.

- What is the size of EEPROM? 32Kbytes? :  64 KB

- What is the size of DDR RAM? : 256 MB

 

Regards,

Kamal Kumar

See Answer In Context

Reply
Replies 7
Adrian_Dicea
Adrian_Dicea Champion
Champion

Posted: ‎2016-02-25 01:41 AM

0 Likes
0
2958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-25 01:41 AM

Link150 does not offer data logging.

Reply
sesa379798
sesa379798 Leader
Leader

Posted: ‎2016-02-26 10:00 AM

0 Likes
5
2958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-26 10:00 AM

but the internal memory?

Reply
KuanKhoon
KuanKhoon Mentor
Mentor

Posted: ‎2016-03-01 08:43 AM

0 Likes
4
2958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-01 08:43 AM

The Link150 does not have user accessible internal memory as it does not have datalogging function. It only gives functional status of the boot memory, EEPROM and DDR RAM. For more information, please refer to the user manual link below,

www2.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/276000/FA276295/en_US/EGX150UserGuide.pdf

Best Regards,

Tan Kuan Khoon

Senior Specialist

Product Application & Engineering

Schneider Electric Singapore

Reply
Adrian_Dicea
Adrian_Dicea Champion
Champion

Posted: ‎2016-03-07 05:35 AM

0 Likes
3
2958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-07 05:35 AM

To exhaust the subject, can anyone answer, ordered by higher importance:

- What is the filesystem size/free space ?

- What is the size of Ethernet Physical port 1 Reception/Transmission Buffer?

- What is the size of Ethernet Physical port 2 Reception/Transmission Buffer?

- What is the size of EEPROM? 32Kbytes?

- What is the size of DDR RAM?

Reply
Kamal
Kamal Troubleshooter
Troubleshooter

Posted: ‎2016-03-07 10:46 PM . Last Modified: ‎2025-04-09 04:53 AM

2 Likes
2
2959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-07 10:46 PM

Hi Adrian,

Please find the answer

- What is the filesystem size/free space ? : Flash - 128 MB (total), used around (10 MB)

- What is the size of Ethernet Physical port 1 Reception/Transmission Buffer?   : On Application side we support - 32 (tcp connection) * 32 (serial packet ) * 255 bytes of memory.

- What is the size of Ethernet Physical port 2 Reception/Transmission Buffer?  : 32 (tcp connection) * 32 (serial packet ) * 255 bytes of memory.

- What is the size of EEPROM? 32Kbytes? :  64 KB

- What is the size of DDR RAM? : 256 MB

 

Regards,

Kamal Kumar

Reply
Yu_Diao
Yu_Diao Leader
Leader

Posted: ‎2016-03-11 08:08 PM

0 Likes
1
2958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-11 08:08 PM

Kamal KUMAR

You mentioned that the LINK150 supports 32 TCP connections above. But from what I have found out from the user guide, the user can only choose 8 or 16 "TCP/IP Client connections" from the web configuration interface.

Does this mean we will see this option going up to 32 in the future firmware release? It is important when try to replace EGX100, since EGX300 supports 32 connections by default and can be increased to 48 (or 64, don't recall exactly).

Regards,

Attachments
Reply
Kamal
Kamal Troubleshooter
Troubleshooter

Posted: ‎2016-03-11 09:26 PM

1 Like
0
2958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-11 09:26 PM

Yu Diao Yes , in the future release of firmware it is going to support 32 TCP/IP connection as of now it is limited to 8 or16.

Regards,

Kamal Kumar

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore