Use Panel Server as a gateway to have FDM128 displaying Smartlink Modbus

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Use Panel Server as a gateway to have FDM128 displaying Smartlink Modbus
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
98
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
43
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
Jean_Trial
Crewman Jean_Trial
Crewman

Posted: ‎2022-07-05 04:25 AM

0 Likes
2
1514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-05 04:25 AM

Use Panel Server as a gateway to have FDM128 displaying Smartlink Modbus

Hi the experts,

 

I would like to use FDM128 to display information from Smartlink Modbus connected to Panel Server.

FDM128 does support Smartlink Modbus, but PAS v1.3.2 does NOT.

Does that mean I cannot use PAS as a gateway in this case?

 

Could you please confirm?

 

Regards

 

Labels
  • Labels:
  • Product selection
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Szymon_Hochół
Captain Szymon_Hochół Captain
Captain

Posted: ‎2022-07-05 04:48 AM

1 Like
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-05 04:48 AM

Hi @Jean_Trial ,

Panel Server with firmware 1.3.2 can be used for such application. Lack of support for Smartlink Modbus in PAS v1.3.2 means that it will not be possible to view Smartlink’s data in PAS embedded webpages, but the Modbus Gateway feature works for all Modbus RTU devices connected to it (supported, not supported, 3rd party). In that case you can connect your Smartlink to serial port of PAS and then connect PAS with FDM128 in the same Ethernet network. FDM should read Smartlink’s registers directly, using PAS as a transparent gateway.

 

Best regards

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2022-07-05 04:58 AM

3 Likes
0
1505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-05 04:58 AM

Hello @Jean_Trial , 

I confirm this is working well with PAS600 v001.003.002 + FDM128 v8.0.28.

 

My architecture is the following:

  1. FDM128 connected to an ETH Switch
  2. PAS600L connected to the same ETH Switch
  3. Smartlink Modbus connected to the Serial Port of the PAS600L
  4. Reflex iC60 and Acti9 MCB connected to the IO Channels of the Smartlink Modbus

With this architecture I can view the status of the OF/SD on the FDM128 screen and I can also control my Reflex iC60.

Capture d’écran 2022-07-05 135805.jpg 

 

I recommend to have:

  • Panel Server upgraded to 001.003.002
  • FDM128 upgraded to v8.0.30

Regards, 

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Szymon_Hochół
Captain Szymon_Hochół Captain
Captain

Posted: ‎2022-07-05 04:48 AM

1 Like
0
1510
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-05 04:48 AM

Hi @Jean_Trial ,

Panel Server with firmware 1.3.2 can be used for such application. Lack of support for Smartlink Modbus in PAS v1.3.2 means that it will not be possible to view Smartlink’s data in PAS embedded webpages, but the Modbus Gateway feature works for all Modbus RTU devices connected to it (supported, not supported, 3rd party). In that case you can connect your Smartlink to serial port of PAS and then connect PAS with FDM128 in the same Ethernet network. FDM should read Smartlink’s registers directly, using PAS as a transparent gateway.

 

Best regards

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2022-07-05 04:58 AM

3 Likes
0
1506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-05 04:58 AM

Hello @Jean_Trial , 

I confirm this is working well with PAS600 v001.003.002 + FDM128 v8.0.28.

 

My architecture is the following:

  1. FDM128 connected to an ETH Switch
  2. PAS600L connected to the same ETH Switch
  3. Smartlink Modbus connected to the Serial Port of the PAS600L
  4. Reflex iC60 and Acti9 MCB connected to the IO Channels of the Smartlink Modbus

With this architecture I can view the status of the OF/SD on the FDM128 screen and I can also control my Reflex iC60.

Capture d’écran 2022-07-05 135805.jpg 

 

I recommend to have:

  • Panel Server upgraded to 001.003.002
  • FDM128 upgraded to v8.0.30

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of