Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
28 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Dear all,
For developing some wireless solutions, we've been wondering if Panel Server can connect to Telemecanique Limit Switches such as XCKJ10541 (or similar).
Thanks in advance!
BR.
Link copied. Please paste this link to share this article on your social media post.
Hello Katherine,
wireless Limit Switch XCKJ10541 is not supported by Panel Server,
The best way to know if a wireless is supported by Panel Server is to refer to the release note which embed the list of supported product
PAS600: DOCA0178EN-xx (currently, xx=03 for the last version)
PAS800: DOCA0248EN-xx (currently, xx=00 for the last version)
BR
Link copied. Please paste this link to share this article on your social media post.
Hello @kaenriquezr ,
The XCKJrange from Industry is not a wireless sensor. We need more precision about the goal of your system.
It may be possible to connect the NC/NO output of the sensor to the Digital Inputs of a PAS600L or PAS800L (each gateway has only 2x DI). You must ensure that the sensor can support 24DC voltage.
Once you have connected the XCKJ to the DI of the Panel Server you can commission the DI with EcoStruxure Power Commission (DI commissioning with Web Pages will come later).
DI status can be viewer on EPC and are also available through Modbus Registers.
Regards,
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.