Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82523members
350127posts

Use Panel Server as a gateway to have FDM128 displaying Smartlink Modbus

Gateways and Energy Servers

Get expert answers to your questions regarding Schneider Electric Gateways & Energy Servers, from product selection to implementation and troubleshooting. Collaborate with a global community of experts and peers, get support and share your experiences by subscribing to the Schneider Electric Community Gateways and Energy Servers forum today.

Solved
Jean_Trial
Crewman
Crewman
0 Likes
2
304

Use Panel Server as a gateway to have FDM128 displaying Smartlink Modbus

Hi the experts,

 

I would like to use FDM128 to display information from Smartlink Modbus connected to Panel Server.

FDM128 does support Smartlink Modbus, but PAS v1.3.2 does NOT.

Does that mean I cannot use PAS as a gateway in this case?

 

Could you please confirm?

 

Regards

 

Tags (1)

Accepted Solutions
Szymon_Hochół
Commander Commander
Commander

Re: Use Panel Server as a gateway to have FDM128 displaying Smartlink Modbus

Hi @Jean_Trial ,

Panel Server with firmware 1.3.2 can be used for such application. Lack of support for Smartlink Modbus in PAS v1.3.2 means that it will not be possible to view Smartlink’s data in PAS embedded webpages, but the Modbus Gateway feature works for all Modbus RTU devices connected to it (supported, not supported, 3rd party). In that case you can connect your Smartlink to serial port of PAS and then connect PAS with FDM128 in the same Ethernet network. FDM should read Smartlink’s registers directly, using PAS as a transparent gateway.

 

Best regards

See Answer In Context

Tags (1)
Romain_Polette
Sisko Sisko
Sisko

Re: Use Panel Server as a gateway to have FDM128 displaying Smartlink Modbus

Hello @Jean_Trial , 

I confirm this is working well with PAS600 v001.003.002 + FDM128 v8.0.28.

 

My architecture is the following:

  1. FDM128 connected to an ETH Switch
  2. PAS600L connected to the same ETH Switch
  3. Smartlink Modbus connected to the Serial Port of the PAS600L
  4. Reflex iC60 and Acti9 MCB connected to the IO Channels of the Smartlink Modbus

With this architecture I can view the status of the OF/SD on the FDM128 screen and I can also control my Reflex iC60.

Capture d’écran 2022-07-05 135805.jpg 

 

I recommend to have:

  • Panel Server upgraded to 001.003.002
  • FDM128 upgraded to v8.0.30

Regards, 

 

Romain POLETTE - Global Expert Technical Support - Digital Power Division
38EQI - Eybens - France

See Answer In Context

Tags (1)
2 Replies 2
Szymon_Hochół
Commander Commander
Commander

Re: Use Panel Server as a gateway to have FDM128 displaying Smartlink Modbus

Hi @Jean_Trial ,

Panel Server with firmware 1.3.2 can be used for such application. Lack of support for Smartlink Modbus in PAS v1.3.2 means that it will not be possible to view Smartlink’s data in PAS embedded webpages, but the Modbus Gateway feature works for all Modbus RTU devices connected to it (supported, not supported, 3rd party). In that case you can connect your Smartlink to serial port of PAS and then connect PAS with FDM128 in the same Ethernet network. FDM should read Smartlink’s registers directly, using PAS as a transparent gateway.

 

Best regards

Tags (1)
Romain_Polette
Sisko Sisko
Sisko

Re: Use Panel Server as a gateway to have FDM128 displaying Smartlink Modbus

Hello @Jean_Trial , 

I confirm this is working well with PAS600 v001.003.002 + FDM128 v8.0.28.

 

My architecture is the following:

  1. FDM128 connected to an ETH Switch
  2. PAS600L connected to the same ETH Switch
  3. Smartlink Modbus connected to the Serial Port of the PAS600L
  4. Reflex iC60 and Acti9 MCB connected to the IO Channels of the Smartlink Modbus

With this architecture I can view the status of the OF/SD on the FDM128 screen and I can also control my Reflex iC60.

Capture d’écran 2022-07-05 135805.jpg 

 

I recommend to have:

  • Panel Server upgraded to 001.003.002
  • FDM128 upgraded to v8.0.30

Regards, 

 

Romain POLETTE - Global Expert Technical Support - Digital Power Division
38EQI - Eybens - France
Tags (1)