Hi Sir/Madam,
I failed to configure the device's time in Com'X 510.
The device's time did not change even when I saved the current time in Date/Time Settings page.
Could you please help?
Best regards,
Janet
Link copied. Please paste this link to share this article on your social media post.
Hi Janet,
If you have a backup file for this Com'X, you can apply it and your settings will be restored.
Let me know if you need further assistance.
Randi
Link copied. Please paste this link to share this article on your social media post.
Hello @Janet_lau ,
This is working well on my Com'X510 v6.8.4.
I confirm there is a gap. When I change the date / time, sometime it can take more that 10 sec to be updated on the interface.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hi Romain,
Thank you for your reply.
I tried to configured a new time to Com'X 510 again and waited for at least 1 minute, yet there was no update on the Com'X 510 time.
Many thanks.
Best regards,
Janet
Link copied. Please paste this link to share this article on your social media post.
There is an update on the time configuration issue on Com'X 510.
Once I reset the Com'X into Factory setting, the time can be changed and saved again, yet I lost all the device setting in Com'X.
Link copied. Please paste this link to share this article on your social media post.
Hi Janet,
If you have a backup file for this Com'X, you can apply it and your settings will be restored.
Let me know if you need further assistance.
Randi