Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

ULP Systems for NSX

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • ULP Systems for NSX
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
107
Guillaume_Evrard
Captain Guillaume_Evrard Captain
52
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
32
View All
Related Products
product field
Schneider Electric
ComPacT NSX, new generation

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
jedzruiz1985
Lieutenant JG jedzruiz1985
Lieutenant JG

Posted: ‎2025-07-01 08:43 PM . Last Modified: ‎2025-07-01 08:45 PM

0 Likes
3
181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-01 08:43 PM

ULP Systems for NSX

Hi Xperts,

 

Just want to ask your expert opinion. Where to install TRV00880 if you have IFE stacked with multiple IFMs.

 

Is it in the unused port of the last IFM on the chain only. 

 

or

 

Is it on every unused port of every IFMs and the chain and IFE server.

 

Thanks in advance

 

 

 

  • Thumbnail of ComPacT NSX, new generation
    Schneider Electric
    ComPacT NSX, new generation
View products (1)
Labels
  • Labels:
  • Legacy Gateways & Energy Servers
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-07-02 12:29 AM

1 Like
0
174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-02 12:29 AM

Hello @jedzruiz1985 , 

Please have a look on the ULP System Guide dedicated page:

https://www.productinfo.schneider-electric.com/ulp_system_guide/doca0093-ulp-system-user-guide/Engli...

 

For future reference, keep in mind there is a new ref of BSCM (S434220) that can communicate directly through Modbus.

 

ULP is a serial protocol and you need a termination at each end of the bus. It means you need an ULP termination on the 2nd ULP port of each IFM. ULP protocol is not chained through stacked IFM (only 24DC and Modbus RS485).

Regards, 

 

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 3
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-07-02 12:29 AM

1 Like
0
175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-02 12:29 AM

Hello @jedzruiz1985 , 

Please have a look on the ULP System Guide dedicated page:

https://www.productinfo.schneider-electric.com/ulp_system_guide/doca0093-ulp-system-user-guide/Engli...

 

For future reference, keep in mind there is a new ref of BSCM (S434220) that can communicate directly through Modbus.

 

ULP is a serial protocol and you need a termination at each end of the bus. It means you need an ULP termination on the 2nd ULP port of each IFM. ULP protocol is not chained through stacked IFM (only 24DC and Modbus RS485).

Regards, 

 

 

Romain POLETTE
Solution Architect - France Operations
Reply
jedzruiz1985
Lieutenant JG jedzruiz1985
Lieutenant JG

Posted: ‎2025-07-02 04:08 PM

0 Likes
0
166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-02 04:08 PM

Hi Romain,

 

Thanks for making it clear because publication is saying 1 at the last IFM and I saw aswell a diagram showing at each IFM and IFE.

 

So, it is 1 per unused port of the IFM and IFE then. 

 

Thanks a lot.

 

Regards,

 

Jiedan

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-07-02 09:32 PM

0 Likes
0
164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-02 09:32 PM

hello @jedzruiz1985 ,

Might be a confusion between modbus RJ45 line termination and ULP RJ45 termination. As explained one ULP termination at each unused ULP port except on eIFE for MTZ where the termination is integrated.

Kind Regards

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore