Smartlink SI D can't login

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Smartlink SI D can't login
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Bygg
Crewman Bygg
Crewman

Posted: ‎2024-07-08 03:16 AM

0 Likes
4
1097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-08 03:16 AM

Smartlink SI D can't login

Hello, I have problems logging in to smartlink IS D, after updating to the latest firmware, I think it was V2.4.6 with EcoStruxure power Commission 
Does anyone know, if the username and password have been changed
from default admin/admin

Attachments
Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-07-09 01:21 AM

0 Likes
1
1068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-09 01:21 AM

Hello @Bygg , 

 

Not a good news... there is a chance that your device is corrupted.

 

Did you upgraded the device in peer to peer ? Or through a Network with routers ?

 

To confirm the issue you can read the Modbus Registers address 109 (Register Number = 110):

Romain_Polette_0-1720513146486.png

If the result is not V2.4.6, this may confirm that the exploit file of your device was not pushed correctly during the FW upgrade process.

 

In this case, please contact tech support for further instruction.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 4
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-07-09 01:21 AM

0 Likes
1
1069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-09 01:21 AM

Hello @Bygg , 

 

Not a good news... there is a chance that your device is corrupted.

 

Did you upgraded the device in peer to peer ? Or through a Network with routers ?

 

To confirm the issue you can read the Modbus Registers address 109 (Register Number = 110):

Romain_Polette_0-1720513146486.png

If the result is not V2.4.6, this may confirm that the exploit file of your device was not pushed correctly during the FW upgrade process.

 

In this case, please contact tech support for further instruction.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Bygg
Crewman Bygg
Crewman

Posted: ‎2024-07-11 01:18 AM

0 Likes
0
1033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-11 01:18 AM

Hi, @Romain_Polette 

Thanks for your reply, 
We have chosen to change the Smartlink to Power tag link.

Think it's the safest bet for the future.

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-07-11 04:13 AM

0 Likes
1
1029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-11 04:13 AM

Hello @Bygg , 

PowerTag Link is discontinued (no new feature / FW development) but maybe you have some stock in your country. For new design (or retrofit) we recommend Panel Server PAS400 to replace Smartlink SID and PowerTag Link A9XMWD20.

 

If you replace your gateway, you will need to power off/on your PowerTag sensors to pair them with your new gateway.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Bygg
Crewman Bygg
Crewman

Posted: ‎2024-07-11 05:00 AM

1 Like
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-11 05:00 AM

Hello @Romain_Polette 
okay, we have started to switch from Smartlink to powertag link, so now we should probably consider Psa400, thanks for the info 🙂

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore