I can't connect the two PM5560 measuring devices to the server panel via EPC. The connection is a Modbus line connection with an end-of-line resistor at one of the measuring devices. I have already configured both PM5560 measuring devices at 9600 baud with odd parity. I still can't see the two PM5560 measuring devices on the Ecostruxure Power Commission platform. Thank you for your help.
Link copied. Please paste this link to share this article on your social media post.
Hello @Sidym ,
can you detect both PM5560 on your Panel Server Web interface ?
If yes, did you enable Modbus TCP services on your Panel Server ?
Please check the Virtual IDs of your PM5560 attributed by the Panel Server to your devices. On EPC, please use Panel Server IP + Virtual IDs to detect the devices.
EPC supports PM5560 with FW 2.7.4 or higher, check your PM5560 version.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello,
I understand that you have wired PM to PAS using RS485 modbus interface. Are you sure of the +/- wiring.
Have you configured the modbus port on PAS to match the modbus config of your PM ?
Are you sure you have modbus Id configured on PM ?
Are you adding the PM manually or are you trying to discover them in PAS ?
You have to configure this page in PAS web pages :