PM5560 modbus RTU with Panel Server

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • PM5560 modbus RTU with Panel Server
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
96
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
41
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Power Commission

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Sidym
Sidym
Cadet

Posted: ‎2024-07-04 05:13 AM

0 Likes
3
422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-04 05:13 AM

PM5560 modbus RTU with Panel Server

I can't connect the two PM5560 measuring devices to the server panel via EPC. The connection is a Modbus line connection with an end-of-line resistor at one of the measuring devices. I have already configured both PM5560 measuring devices at 9600 baud with odd parity. I still can't see the two PM5560 measuring devices on the Ecostruxure Power Commission platform. Thank you for your help.

  • Thumbnail of EcoStruxure™ Power Commission
    Schneider Electric
    EcoStruxure™ Power Commission
View products (1)
Labels
  • Labels:
  • Commissioning
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2024-07-04 05:32 AM

0 Likes
2
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-04 05:32 AM

Hello @Sidym , 

can you detect both PM5560 on your Panel Server Web interface ?

If yes, did you enable Modbus TCP services on your Panel Server ?

Please check the Virtual IDs of your PM5560 attributed by the Panel Server to your devices. On EPC, please use Panel Server IP + Virtual IDs to detect the devices.

EPC supports PM5560 with FW 2.7.4 or higher, check your PM5560 version.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Sidym
Sidym
Cadet

Posted: ‎2024-07-04 06:04 AM

0 Likes
1
419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-04 06:04 AM

Hi @Romain_Polette, 

 

Thanks for your responsiveness,

 

I can't even detect a single PM5560

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-07-04 08:43 PM

0 Likes
0
376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-04 08:43 PM

Hello,

 

I understand that you have wired PM to PAS using RS485 modbus interface. Are you sure of the +/- wiring.

Have you configured the modbus port on PAS to match the modbus config of your PM ?

Are you sure you have modbus Id configured on PM ?

Are you adding the PM manually or are you trying to discover them in PAS ?

You have to configure this page in PAS web pages : 

Guillaume_Evrard_0-1720150981866.png

 

Kind Regards,

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of