Is the PAS800 compatible with ST6 HMI?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @aespinoza_eicsa ,
Guillaume's right. For the moment only the Web HMI from 3rd party manufacturer has been validated for use with Panel Server installed on OKKEN (but should also work in Prisma). It means this Web HMI has been tested in our EcoStruxure Lab (screen resolution, formatting, ergonomic, response time, temperature). This Web HMI is also less expensive than our industrial HMI.
Only Harmony HMIST6W6xxx seems to be Web HMI and then could work with Panel Server. But you have no guarantee this will be full compatible with PAS800 Web Services.
Regards,