Hi everyone!
I hope you're doing well.
I have a client who can´t enter to EBX510's web interface using Google Chrome. It does work with Explorer though.
The error is:" ERR_SSL_VERSION_OR_CIPHER_MISMATCH".
We already tried to delete browser cache and cookies.
I´m attaching an image of this problem.
Best regards.
Link copied. Please paste this link to share this article on your social media post.
Hi,
This is as a result of the Com'X running out of date firmware. Please use the USB firmware update method to update the Com'X firmware to version 6.8.4
Randi
Link copied. Please paste this link to share this article on your social media post.
Hi,
This is as a result of the Com'X running out of date firmware. Please use the USB firmware update method to update the Com'X firmware to version 6.8.4
Randi
Link copied. Please paste this link to share this article on your social media post.
Hello everyone,
I'm having the same problems, but when I try to upgrade the firmware via USB, the com'x510 never changes LED color from orange to green after more than 1 hour of rebooting.
Do you have any recommendations?
Regards
Link copied. Please paste this link to share this article on your social media post.
Hi,
You may have to factory reset it. You can save the configuration before resetting via the USB port: