Pulse metering
Hi Xperts,
I would like to ask, if we have 29 PM3250 meters and 8 pulse meters for water, and we need them to be logged on a panel server and have the option for Ecostruxure Energy Hub, what would be the best cost effective way to gather the data from the pulse meters and the whole system will be ready for Energy Hub?
My take on this is 2 Panel servers,
1 will handle 20 PM3250 meters (based on EEH load calculator for a PM3xxx meter)
1 will handle 9 PM3250 meters and the 8 pulse meters via smartlink
Will Energy Hub be able to see the pulse meters being connected to a smartlink or meters with digital inputs? This is an inquiry because I have heard from someone before that EEH only works with pulse meters connected directly to the PAS.