PROBLEM WITH PAS600 AND POWERTAG RECONNECTION

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • PROBLEM WITH PAS600 AND POWERTAG RECONNECTION
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
nicolasjacome
Ensign nicolasjacome
Ensign

Posted: ‎2024-11-25 07:11 AM

0 Likes
3
1219
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-25 07:11 AM

PROBLEM WITH PAS600 AND POWERTAG RECONNECTION

Hi all,

 

I am having trouble with a project involving a PAS600 Gateway and 5 NSX type PowerTags. We have installed 2 identical smart panels in a datacenter which are separated by around 15 inches from each other, you can see the layout in the picture below:

 

nicolasjacome_0-1732546265332.png

 

Each PAS600 (one on each panel) is connected to a Power Meter and a PLC via Modbus RTU and to an HMI via Modbus TCP. We have 3 TH110 sensors and 5 PowerTags connected as wireless devices.

 

Currently, we are having energy cuts due to a power crisis nationwide, so the panels lose energy 4 times a day for around 40-50 seconds. When the energy comes back (from the grid or a generator) some of the PowerTag sensos from both panels lose connection to the PAS600 and do not reconnect again. The communication via Modbus RTU and TCP does not seem affected, as well as the link to the TH110 sensors. It is only the PowerTags that have this problem.

 

We tried to solve this issue by connecting the PAS600 to a UPS in order to avoid it from powering off, but the problem keeps happening. The thing is that it is not the same sensors that lose connection every time, it seems to be random how many reconnect and which of them do not. One time we even waited around 20 minutes and all 5 sensors reconnected by themselves, but this has only happened once.

 

We are unsure whether this happens because of both panels being so close to each other and the requests from all 10 sensors interfere with each other and each PAS600 when the power is restablished, maybe the PowerTag sensors are not supposed to be powered on all simultaneously, or maybe it is because all 5 PowerTag sensors are too close to each other on each panel.

 

If anyone has seen this happen before I would appretiate any help that you can give me. 

 

Thanks for the help!

Labels
  • Labels:
  • PowerTag Energy
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Mark_Raftery
Ensign Mark_Raftery Ensign
Ensign

Posted: ‎2024-11-25 11:37 PM

1 Like
1
1185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-25 11:37 PM

Good morning,

You didn't mention the PowerTag type, or the Firmware Version of the PaS, currently V2.0.0

But that aside did you leave the Wireless Chanel Selection Mode in Automatic or select different channels for each PaS?

Have a look at Wireless Communication Architectures With EcoStruxure Panel Server Design Guide.

Consider if you havent already to select different channels for each PaS, I had a similar issue when commissioning PT and the PaS found the Distribution board above through a concrete floor and the DB metal enclosure doors shut.

Just a thought.

KRF Mark

KRF Mark

Attachments
Reply
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2024-11-25 11:44 PM

0 Likes
0
1183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-25 11:44 PM

Hello @nicolasjacome 
As you have already contacted the Customer Care Center (CCC) for this issue., we are currently working  on it and will come back to you using this official technical support channel.
Regards
Eric

Reply
nicolasjacome
Ensign nicolasjacome
Ensign

Posted: ‎2024-11-26 06:05 AM

1 Like
0
1152
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-26 06:05 AM

Hi Mark,

Thanks for the tips, however we already did all that. We set each PAS to channels 8 and 23 respectively and still we had the same issue. 

We are going to try updating the firmware version as we were using just one previous to V2.0.0.

The type of powertag used is LV434023. Would you say it is normal for them to stop connecting to the PAS for any reason at all? We are considering sending the powertags back and apply the warranty as we do not seem to get them working.

 

@Eric_HAVAS yes, we have also escalated this to CCC, but I want to keep this open just in case someone else has come across this situation.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.