Adding PowerTag A9MEM1540 to PAS600 Gateway

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Adding PowerTag A9MEM1540 to PAS600 Gateway
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
108
Guillaume_Evrard
Captain Guillaume_Evrard Captain
52
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
32
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
ArcherWang
Lieutenant | EcoXpert Master ArcherWang Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-01-17 01:59 PM

0 Likes
7
2490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-17 01:59 PM

Adding PowerTag A9MEM1540 to PAS600 Gateway

Hi Huys,

 

I hope you're doing well.

 

My customer has opted to replace the old PowerTag Link Concentrator with a PAS600. I'm currently tasked with searching for and adding the Wireless PowerTags to the new PAS600 gateway, as shown in the photo below. However, it appears that nothing can be selected.

I'm working on this remotely through an RDP session for my customer. Any guidance on how to activate the discovery mode/add devices would be greatly appreciated. 

 

ArcherWang_0-1705528009743.png

 

Labels
  • Labels:
  • Legacy Gateways & Energy Servers
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-01-18 01:03 AM

0 Likes
3
2460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-18 01:03 AM

Hi @ArcherWang , 

As mentioned by Guillaume, please first check that your PowerTag sensor front LED is blinking fast orange.

If not blinking orange, it means that the PowerTag sensor is not ready to be paired with Panel Server.

 

In this case:

  • If PowerTag sensor is blinking fast red, you need to power off/on the sensor to put it in pairing mode (blinking orange)
  • If PowerTag sensor is blinking slow red or slow green, it means that the sensor is paired with another gateway

Regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2024-01-22 08:48 PM

1 Like
1
2435
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-22 08:48 PM

Hello, I let @Romain_Polette answer but his previous answer seems to confirm that if the gateway has disappeared and not able to communicate with the gateway (blinking fast red) you have to power off/on to reset it and be able to pair to a new gateway.

If you can unpair it should allow to pair it without requiring reset,

 

Kind Regards

See Answer In Context

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-01-23 12:15 AM . Last Modified: ‎2024-01-23 12:18 AM

0 Likes
1
2429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-23 12:15 AM

Hello @ArcherWang , 

 

My answers in red below.

 

"If a sensor has been previously paired with a PowerTag Link (PTL) and is now being replaced with a PAS600, should I unpair the sensors before scanning them with the PAS?"

=> Yes this is the best practice. But it can depend on your case...

=> Case 1: both PTL and PAS600 are on or PTL is on - PAS600 is off:

  • In this case the PowerTag sensors may be still paired with the PTL.
  • Check that the PTag sensors are blinking slow green (every 5 sec or more).
  • Open your PTL web services (or connect the PTL to EcoStruxure Power Commission (EPC)).
  • Unpair the PTag sensors from the PTL
  • Check that the PTag sensors are now blinking fast orange
  • You can pair the Ptag with your PAS600

=> Case 2 : PTL is off - PAS600 is on:

  • If the PTag sensors are blinking fast red it means that the sensors have lost the communication with the PTL for more than 300 sec (issue with gateway detected).
  • if both PTL and PAS600 are mounted on the same panel, you can try power on the PTL. Then, PTag sensors should retrieve the communication with PTL after 1 or 2 minutes (blinking slow green). Follow case 1 to unpair sensors from the PTL.
  • If the PTL was removed from the panel or if the PTag sensors are still blinking fast red, read my answer bellow

"Or is there a method to reset the sensors?"

=> You cannot "soft reboot" the PowerTag sensors (no front face button or restart feature integrated in the gateways). The only way to restart this sensor is to power it off/on (open/close the associate breaker). After a power off/on, the Ptag sensor should blink fast orange (ready for pairing process). 

 

Regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 7
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2024-01-17 09:05 PM

0 Likes
0
2479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-17 09:05 PM

Hello,

Personaly I do not use EPC, I am using the web pages. Is the Zigbee wireless network activated on the PAS ?

Normally you should launch the discovery and pair your powertag locally. If the powertag was paired to the PTL you  might have to unpair/reset it if similar to other zigbee devices but I do not use them.

A9MEM1540 is in the release not since 1.3.2, so it is supported.

Maybe you have to check the Led indication on Powertag to identify the status.

Kind Regards

 

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-01-18 01:03 AM

0 Likes
3
2461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-18 01:03 AM

Hi @ArcherWang , 

As mentioned by Guillaume, please first check that your PowerTag sensor front LED is blinking fast orange.

If not blinking orange, it means that the PowerTag sensor is not ready to be paired with Panel Server.

 

In this case:

  • If PowerTag sensor is blinking fast red, you need to power off/on the sensor to put it in pairing mode (blinking orange)
  • If PowerTag sensor is blinking slow red or slow green, it means that the sensor is paired with another gateway

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
ArcherWang
Lieutenant | EcoXpert Master ArcherWang Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-01-22 05:40 PM

0 Likes
2
2440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-22 05:40 PM

Thanks for your reply.

Thank you for your response.

In the second scenario, if a sensor had been previously paired with a PowerTag Link and is now being replaced with a PAS600, should I unpair the sensors before scanning them with the PAS? Or is there a method to reset the sensors?

 

Kind regards,

Archer

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2024-01-22 08:48 PM

1 Like
1
2436
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-22 08:48 PM

Hello, I let @Romain_Polette answer but his previous answer seems to confirm that if the gateway has disappeared and not able to communicate with the gateway (blinking fast red) you have to power off/on to reset it and be able to pair to a new gateway.

If you can unpair it should allow to pair it without requiring reset,

 

Kind Regards

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-01-23 12:15 AM . Last Modified: ‎2024-01-23 12:18 AM

0 Likes
1
2430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-23 12:15 AM

Hello @ArcherWang , 

 

My answers in red below.

 

"If a sensor has been previously paired with a PowerTag Link (PTL) and is now being replaced with a PAS600, should I unpair the sensors before scanning them with the PAS?"

=> Yes this is the best practice. But it can depend on your case...

=> Case 1: both PTL and PAS600 are on or PTL is on - PAS600 is off:

  • In this case the PowerTag sensors may be still paired with the PTL.
  • Check that the PTag sensors are blinking slow green (every 5 sec or more).
  • Open your PTL web services (or connect the PTL to EcoStruxure Power Commission (EPC)).
  • Unpair the PTag sensors from the PTL
  • Check that the PTag sensors are now blinking fast orange
  • You can pair the Ptag with your PAS600

=> Case 2 : PTL is off - PAS600 is on:

  • If the PTag sensors are blinking fast red it means that the sensors have lost the communication with the PTL for more than 300 sec (issue with gateway detected).
  • if both PTL and PAS600 are mounted on the same panel, you can try power on the PTL. Then, PTag sensors should retrieve the communication with PTL after 1 or 2 minutes (blinking slow green). Follow case 1 to unpair sensors from the PTL.
  • If the PTL was removed from the panel or if the PTag sensors are still blinking fast red, read my answer bellow

"Or is there a method to reset the sensors?"

=> You cannot "soft reboot" the PowerTag sensors (no front face button or restart feature integrated in the gateways). The only way to restart this sensor is to power it off/on (open/close the associate breaker). After a power off/on, the Ptag sensor should blink fast orange (ready for pairing process). 

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
ArcherWang
Lieutenant | EcoXpert Master ArcherWang Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-01-24 02:55 PM

0 Likes
0
2401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-24 02:55 PM

Thank you very much for your response. I've been seeking detailed information because the PowerTags are connected to Circuit Breakers (CBs) in the main switchboard of a building. Rebooting the PowerTags would necessitate a brief power outage for the building, and I wanted to ensure that I have all the necessary information to coordinate this outage window effectively.

 

Kind regards,

Archer

Reply
Dayana_Herrera
Dayana_Herrera
Cadet

Posted: ‎2024-11-24 07:17 PM

0 Likes
0
1487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-24 07:17 PM

Please in my project every time there is a power outage the power tags get disconnected from the pass 600L and do not reconnect automatically even though the PASS 600L does not turn off because it is backed up by UPS.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore