Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Search in
Link copied. Please paste this link to share this article on your social media post.
I want to log several parameter of my PM5350 using PAS800L, because of PM5350 did not detected on PAS800L, i got custom model addition and Import it form EPC - W, however after the template has successfully added, my PM5350 still did not detected by PAS800L, can anyone help me please. My PM5350 has been discover as ID = 1
Link copied. Please paste this link to share this article on your social media post.
Hello,
Are you using discovery to add your PM ? If yes you have to add your PM manually using the custom model you have loaded.
Discovery should detect an unknown device at slave ID 1 as you mention.
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Thank you so much for your help, it works, now I can Log PM5350 using PAS800L
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.