Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
30 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Given a PowerTag of the following serial number:
RN-####-###-4-GH-0105
And we query the modbus section for this tag's serial:
Then we get
RN-####-###-4-GH-010
instead of the full serial number.
Presumably this is because the maximum length of this section is 20 bytes, whilst the actual serial number contains 21 characters. Is there a workaround for this?
Link copied. Please paste this link to share this article on your social media post.
Hello @Breina
Thank you to have raised this point, R&D has been notified of this issue.
Link copied. Please paste this link to share this article on your social media post.
Hello @Breina
Hope you're fine.
Can you please provide a similar screenshot of the below one. I was not able to find in my config a device serial number with more than 20 chars.
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Hey Eric,
Here you go:
Please forgive me censoring 7 characters, this device is not mine so I don't want to leak his serial number.
Link copied. Please paste this link to share this article on your social media post.
Hello @Breina ,
I confirm, I can reproduce with a recent PTag NSX (SN = 21 char).
Value returned by Modbus Tool (only 20 char as expected):
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @Breina
Thank you to have raised this point, R&D has been notified of this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.