Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Hi
In a installation with PAS600 and IEEE 802.15.4 wireless communication with PowerTag Energy sensors. Now the installation should be extended with TH110/CL110 environmental sensors placed outside the cabinet with longer distances between PAS and the environmental sensors.
We will replace the PAS600 with PAS800 to have the possibility to use external antenna (according to DOCA0289EN Wireless Communication Architectures With EcoStruxure Panel Server-Design Guide)
Is there a possibility migrate/save a configuration, settings from all existing PowerTag in PAS600 and transfer to PAS800 ?
BR/Anders
Link copied. Please paste this link to share this article on your social media post.
Hello Anders,
Restore function apply on the same model of panel server:
Extract from PaS User guide DOCA0172EN-09 page 110:
"the configuration of a Panel Server can be saved into a file and used to restore the configuration in a Panel Server of the same model, or the same Panel Server."
Link copied. Please paste this link to share this article on your social media post.
Hello Anders,
Restore function apply on the same model of panel server:
Extract from PaS User guide DOCA0172EN-09 page 110:
"the configuration of a Panel Server can be saved into a file and used to restore the configuration in a Panel Server of the same model, or the same Panel Server."
Link copied. Please paste this link to share this article on your social media post.
Hello Eric
Thanks for answer, as I understand the user guide PAS600 and PAS800 is not the same model so in this case it is not possible to restore the configuration. All configuration and settings must be done again in the new PAS800
BR/Anders
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.