Hi
Our new 1-phase energy meter A9MEM2455 will it be a supported device in coming firmware ?, for local energy server use
BR/Anders
Link copied. Please paste this link to share this article on your social media post.
Hi Anders @AndersDahlskog
As of now with PAS FW 001.0007.000, this energy meter A9MEM2455 is not supported. Not sure on the future release support.
Device supported by PAS 800 in FW 1.7.0 https://www.productinfo.schneider-electric.com/ecostruxurepanelserveradvancedrn/doca0248-ecostruxure...
Right now only way to use the device is through Custom Device Model through CWP.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Hi Anders @AndersDahlskog
As of now with PAS FW 001.0007.000, this energy meter A9MEM2455 is not supported. Not sure on the future release support.
Device supported by PAS 800 in FW 1.7.0 https://www.productinfo.schneider-electric.com/ecostruxurepanelserveradvancedrn/doca0248-ecostruxure...
Right now only way to use the device is through Custom Device Model through CWP.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Hi
Thanks for reply, we hope for this meter to be supported in future fw release, as it replace A9MEM2155 that is supported.
BR/Anders
Link copied. Please paste this link to share this article on your social media post.
Hi Anders,
Unfortunately I don't have this A9MEM2455 to perform the test, but if this product replaces the A9MEM2155, have you tried to discover it in PaS as a A9MEM2155? You may access now as a workaround and if we are lucky the A9MEM2455 datas!
Link copied. Please paste this link to share this article on your social media post.
@Eric_HAVAS seems according to documentation that there is a +1 offset in the register :
ex active power register 3054 vs 3055... surprising
Link copied. Please paste this link to share this article on your social media post.
Hello @Guillaume_Evrard ,
There is a dedicated topic on Viva Engage:
https://web.yammer.com/main/org/schneider-electric.com/threads/eyJfdHlwZSI6IlRocmVhZCIsImlkIjoiMjIwO...
Regards,
Link copied. Please paste this link to share this article on your social media post.
For People external to SE +1 offset seems to be confirmed between the 2 products.
Link copied. Please paste this link to share this article on your social media post.
I hope that you can consider to make iEM2455 native for PAS800 in future fw release. I thinking when PAS800 is used as a local energy server