Panel Server Modbus Gateway Behavior

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Panel Server Modbus Gateway Behavior
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
EcoStruxure Panel Server Universal

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2023-09-18 09:24 AM . Last Modified: ‎2023-09-18 09:25 AM

0 Likes
3
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-09-18 09:24 AM

Panel Server Modbus Gateway Behavior

Hi All,

 

Would like to know the behavior of Panel Server as a Modbus gateway. According to the User Guide, Panel Server acts as a transparent Modbus-SL to Modbus TCP/IP gateway, that is, it converts Modbus TCP/IP requests received on unit ID X to Modbus-SL requests sent on server ID X.

 

Wondering if now the panel server has multiple TCP/IP clients (e.g. PME and EPO) and both systems are sending requests to the panel server, the panel server would only sends a single request to the downstream SL device or twice?  

 

Thanks

 

Stuart_Cheng_0-1695053923138.png

 

  • Thumbnail of EcoStruxure Panel Server Universal
    Schneider Electric
    EcoStruxure Panel Server Universal
View products (1)
Labels
  • Labels:
  • Commissioning
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-09-19 12:27 AM . Last Modified: ‎2023-09-19 12:33 AM

0 Likes
0
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-09-19 12:27 AM

Hello @Stuart_Cheng , 

 

Each Panel Server client will open a TCP Source port that will communicate with the port 502 (Modbus TCP) of the Panel Server. Panel Server Modbus Gateway feature will buffer each Client request and forward it separately to the same slave.

 

PME and PSO may not have similar driver for your slave devices. It means that the Modbus frames will be different (e.g. not the same number of consecutive registers). Modbus TCP is just an encapsulation of the original Modbus Frame. So, Panel Server will forward 2 different requests to the same slave.

 

regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 3
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-09-19 12:27 AM . Last Modified: ‎2023-09-19 12:33 AM

0 Likes
0
2036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-09-19 12:27 AM

Hello @Stuart_Cheng , 

 

Each Panel Server client will open a TCP Source port that will communicate with the port 502 (Modbus TCP) of the Panel Server. Panel Server Modbus Gateway feature will buffer each Client request and forward it separately to the same slave.

 

PME and PSO may not have similar driver for your slave devices. It means that the Modbus frames will be different (e.g. not the same number of consecutive registers). Modbus TCP is just an encapsulation of the original Modbus Frame. So, Panel Server will forward 2 different requests to the same slave.

 

regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2023-09-20 06:40 AM

0 Likes
0
2010
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-09-20 06:40 AM

Hi @Romain_Polette,

 

Thanks for the information.
I have some questions to follow up. I found the description of Modbus TCP/IP Proxy in the user guide. As you mentioned each TCP/IP client has its own Modbus Frame, wondering how this proxy mechanism works if each client requests different data? Wondering the major difference that makes panel server a TCP/IP proxy but not a Serial proxy.
Thanks

 

Stuart_Cheng_0-1695217112777.png

 

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-09-21 03:06 AM . Last Modified: ‎2023-09-21 06:58 AM

1 Like
0
1994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-09-21 03:06 AM

Hello @Stuart_Cheng , 

In any case, the Modbus frames will never be merged.

Proxy = intermediate. So the Panel Server is a "Serial Proxy" by default.

For answers to the Modbus TCP Proxy, please check the drawings in the "Examples of Modbus Routing" section of the guide.

 

Example of Modbus TCP/IP Requests for Modbus-SL Devices:

Romain_Polette_2-1695282244196.png

 

Panel Server is a transparent gateway for Serial Devices (not declared in the Panel Server interface).

This is the "Serial Proxy" feature you mentioned in your comment. Panel Server is managing the connection between SCADA and Serial Devices.

Upstream system send requests to the Serial devices by addressing them with their physical Modbus ID (Slave ID).

Each Client will open a TCP Source Port and communicate with the Panel Server (Destination Port 502). Panel Server translate the Modbus TCP requests <=> Modbus Serial requests.

 

Example of Modbus TCP/IP Requests for Modbus-SL Devices With Virtual Server ID Different from the Physical Address:

Romain_Polette_3-1695282815728.png

Similar to the previous example, but the Modbus devices are declared in the Panel Server interface, and the Modbus Clients are addressing the Serial Devices with the Virtual ID attributed by the Panel Server.

 

Example of Modbus TCP/IP Requests for Devices in Switched Topology:

Romain_Polette_4-1695283124772.png

In blue => Panel Server is an ETH Switch

Devices are directly addressed by the upstream software. Each Clients (SCADA, BMS, etc.) will open a TCP port to communicate with port 502 of each Modbus TCP device.

 

In orange => Panel Server is a Modbus Proxy

Proxy Mode can be useful in case if a Modbus TCP device accept a very limited number of TCP connection. By example, you have 10x SCADA but your device only accept 4 simultaneous TCP connections. In this case, you may have communication timeout between some SCADA and your Modbus TCP device.

With the Proxy Mode, all transactions will go through the Panel Server. It means that only Panel Server will open 1x TCP port with each device.

Modbus TCP requests from SCADA, BMS are not changed. 

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore