Dear All,
Good day. Since the absence of communication option of PM5100, Is it posible to use the digital output of the said meter's model to comx510 for kWh monitoring via COMX510 web server?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Hi Romain,
No, we are not planning on integrating the PM5100 as a Pulse Meter. I can mention it to the Offer Manager and see if this is something we'd like to add in the future.
Best regards,
Randi
Link copied. Please paste this link to share this article on your social media post.
Hi @XtianPilarcA ,
You can connect the DO of the PM5100 directly on a Digital Input of the Com'X510. Please refer to the Com'X510 IS for wiring instructions.
PM5100 is not natively supported by the current 6.5.5 Com'X510 firmware. You need to create a device based on a Pulse Meter Custom Model. You will need to define what is the Pulse Weight and some other parameters.
@Randi_Dolan Do you know if the next Com'X 510 FW will integrate the PM5100 as a Pulse Meter in the library ?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hi Romain,
No, we are not planning on integrating the PM5100 as a Pulse Meter. I can mention it to the Offer Manager and see if this is something we'd like to add in the future.
Best regards,
Randi