Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
I have two questions relating to the PAS800L:
Link copied. Please paste this link to share this article on your social media post.
Hello Alanna,
Question 1:
There is no custom dashboard in Panel Server but only native dashboard.
However it is possible to dynamically contextualize dashboard with filters ( type of product / type of measurement / comparison mode ...)
If custom dashboard are needed by customer, an edge control system such as ESX PME must be added in the architecture (extra cost to forecast).
Question2:
It is not possible today with firmware 1.3.x or lower to select the web page showed or not showed in Panel server and all the page embeded are permanently reachable with full access.
However a feature of user managment must be added in a next version to offer limited access to some defined users
Best regards
Link copied. Please paste this link to share this article on your social media post.
Hello Alanna,
Question 1:
There is no custom dashboard in Panel Server but only native dashboard.
However it is possible to dynamically contextualize dashboard with filters ( type of product / type of measurement / comparison mode ...)
If custom dashboard are needed by customer, an edge control system such as ESX PME must be added in the architecture (extra cost to forecast).
Question2:
It is not possible today with firmware 1.3.x or lower to select the web page showed or not showed in Panel server and all the page embeded are permanently reachable with full access.
However a feature of user managment must be added in a next version to offer limited access to some defined users
Best regards
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.