Q1a. If using a Com'X210 / Com'X510 as a datalogger with F/W 6.8.4, how many metering devices can be comfortably interfaced to without causing hardware stability issues? Q1b. Is it typical that an energy monitoring system would have one single Com'X configured to log data from serial meters downstream of all Link150s on the network? Q2. Does the Com'X slow down during configuration as each additional meter is added?
Link copied. Please paste this link to share this article on your social media post.
Hello @khatinsek ,
How many meters connected to each Link150 ?
How many Link150 to be aggregated by the Com'X ?
Performances can depend on many parameters:
So if you have a total of 50 Meters with no events, 2x Topics to log every 15 min, publication frequency once a day => this will be fine.
Please check enclosed document for more information about Com'X typical architectures and limits.
Regards,