Dear All!
We have Schneider measurement system installed with several PAS600 and one PAS800, and multiple PM5310 and 5320.
On the trending page i can't see the PM5310, however I think it is configured right (I can access itt directly from the PAS800, see pictures).
Can somebody help what's wrong?
Link copied. Please paste this link to share this article on your social media post.
hello @BZsala
Have you configured data logging in PAS800 for your PM ? It is under setting/ data management
I see that the PAS600 and PAS800 are connected to cloud, can you explain your set-up ?
If PAS800 is configured using a configuration request, data sampling for internal datalogger is controlled by the config request.
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
This is our topology.
Seems like, on the main PAS800, there was not turned on the logging for this device, only on the PAS600 underneath.
However now I can't change it even if I deactivate sampling and cloud sync.