Has Schneider developed a driver for the PAS600L on PME9? I am trying to add Gas, Water and Steam through the PAS600L. I see a driver for the ComX 210 in Management console.
- Labels:
-
troubleshooting
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @nrodriguez ,
No Panel Server driver is in the roadmap for PME.
If you want to use the internal Modbus mapping for the PASx00L DI, you will need to create your own driver with the Device Type Editor.
You can try the enclosed draft of driver I developed many months ago. It seems working, but please note this is not an official driver developed by PME team.
Regards,
Solution Architect - France Operations
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @nrodriguez ,
No Panel Server driver is in the roadmap for PME.
If you want to use the internal Modbus mapping for the PASx00L DI, you will need to create your own driver with the Device Type Editor.
You can try the enclosed draft of driver I developed many months ago. It seems working, but please note this is not an official driver developed by PME team.
Regards,
Solution Architect - France Operations
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thank you for the files, have you developed a diagram for this?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Could you please provide device Driver of EasyPact MVS21430 for PME 2023.
Please find attached image for better understanding