Mixing PM8000 and PM5110 on EGX 150.
Gateways and Energy Servers
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Mixing PM8000 and PM5110 on EGX 150.
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
59
Randi_Dolan
46
Andy_Hubert
Lieutenant Andy_Hubert Lieutenant
Lieutenant
Posted: ‎2021-07-21 07:28 AM
1323
I have a site where we have a number of PM8000s and PM5110 meters on the same modbus network connected to an EGX, and as yet I can't get the PM8000s to communicate, as the only option in PME is ION protocol.
Is this possible, and if so how do I set the EGX for it to work?
Any pointers would be a help.
Andy
Charles_Murison
Picard Charles_Murison Picard
Posted: ‎2021-09-08 09:15 AM
Hello @Andy_Hubert ,
There is a process called ION over modbus. This option is only available when communicating to the PM8000 on the serial port (which you are). The KB link below has more details.
The PDF attached to the case has steps for the setup of both PME and the device. The device's serial port will need to be set to Modbus.
https://www.se.com/ca/en/faqs/FA331587/
Romain_Polette
Kirk
Posted: ‎2021-07-21 08:07 AM
1317
Some questions first:
  1. What protocol did you set in Link150 for your PM8000 Local ID ? PowerLogic or Modbus ?
  2. What protocol did you set inside your PM8000 Serial Port Settings ? ION or Modbus RTU ?
Romain POLETTE
Solution Architect - France Operations
Andy_Hubert
Lieutenant
Posted: ‎2021-07-23 01:32 AM
1311
The PM800 is set to ION, as that is the only option in PME, and I have just upgraded the EGX to the latest firmware so I have the 'ION Pass through' option available.
The EGX is still set as Modbus.
Andy
Charles_Murison